Hello,
I have a problem.
This is my first solar system, first battery set (four T105's, 6V, 24V series). I've been using it for about two years as a power backup system to the grid (failure).
I wired two batteries in my bank with the wrong AWG size cables (I have since wired the whole bank and inverter cables to 2/0AWG THHN welding cable).
The negative pole to the inverter cable was 0AWG, and positive to negative was 0AWG as well. But then for some unknown reason I used a 4AWG to connect tha battery's positive pole to the next one, and that one developed a bad middle cell, that didn't rise over 1.250 in specific gravity on a normal charge when the rest of the bank (and the two other cells in the battery) reached 1.275. The two other cells on this battery behave normally.
The next battery I believe had a 0AWG cable as well connecting it to the bad one, but the positive cable going to the inverter was not 0AWG, it was thinner. I don't remember the AWG.
I was told by a friend this next battery would be the one to start failing, and soon enough it did. I was foolish enough to not change the wires then. This battery, the one with the positive cable to the inverter connected to it, eventually started dropping SG on every cell. Now while the two remaining good batteries go up to 1.300+ SG on an equalization, these two questionable or "bad" batteries don't rise over 1.275-1.280 (at EQ), at which point I ended EQ.
After normal nocturnal use (discharge - I usually do a 30% DOD, about 1.6kw), my "good" batteries go down to 1.250 (all six cells, both batteries), but the questionable cells on the other two batteries vary between 1.225 and 1.210.
For example, on today's charge, my two "good" batteries reached 1.275, whereas the two batteries I very likely killed reach 1.250 in the best cells of the bad bunch, to 1.230 maybe in the worst.
Now. I've been reading on the forum and asking around, and I already know it's a bad idea to add new batteries to an existing battery bank (replacing the two "bad" batteries). So does this mean that I can pretty much throw all of this battery bank in the trash?
I have also since read that it's a bad idea to add a parallel new bank of batteries and still using this one.
So does that mean I'm SOL and have to throw the bank away?
As money is a factor, should I continue to use this bank until all its batteries go bad, however long that may be?
PD. As an ending question, when factoring in the DC amp loads running thu my batteries, do I have to add the house amp draw to the power coming in to the batteries from the controller?
I have a problem.
This is my first solar system, first battery set (four T105's, 6V, 24V series). I've been using it for about two years as a power backup system to the grid (failure).
I wired two batteries in my bank with the wrong AWG size cables (I have since wired the whole bank and inverter cables to 2/0AWG THHN welding cable).
The negative pole to the inverter cable was 0AWG, and positive to negative was 0AWG as well. But then for some unknown reason I used a 4AWG to connect tha battery's positive pole to the next one, and that one developed a bad middle cell, that didn't rise over 1.250 in specific gravity on a normal charge when the rest of the bank (and the two other cells in the battery) reached 1.275. The two other cells on this battery behave normally.
The next battery I believe had a 0AWG cable as well connecting it to the bad one, but the positive cable going to the inverter was not 0AWG, it was thinner. I don't remember the AWG.
I was told by a friend this next battery would be the one to start failing, and soon enough it did. I was foolish enough to not change the wires then. This battery, the one with the positive cable to the inverter connected to it, eventually started dropping SG on every cell. Now while the two remaining good batteries go up to 1.300+ SG on an equalization, these two questionable or "bad" batteries don't rise over 1.275-1.280 (at EQ), at which point I ended EQ.
After normal nocturnal use (discharge - I usually do a 30% DOD, about 1.6kw), my "good" batteries go down to 1.250 (all six cells, both batteries), but the questionable cells on the other two batteries vary between 1.225 and 1.210.
For example, on today's charge, my two "good" batteries reached 1.275, whereas the two batteries I very likely killed reach 1.250 in the best cells of the bad bunch, to 1.230 maybe in the worst.
Now. I've been reading on the forum and asking around, and I already know it's a bad idea to add new batteries to an existing battery bank (replacing the two "bad" batteries). So does this mean that I can pretty much throw all of this battery bank in the trash?
I have also since read that it's a bad idea to add a parallel new bank of batteries and still using this one.
So does that mean I'm SOL and have to throw the bank away?
As money is a factor, should I continue to use this bank until all its batteries go bad, however long that may be?
PD. As an ending question, when factoring in the DC amp loads running thu my batteries, do I have to add the house amp draw to the power coming in to the batteries from the controller?