Hi there,
I'm new to the forum and fairly new to the world of solar so would appreciate advice from you seasoned veterans...
We are off-grid with the following set up:
6 LG390N2T panels wired in 2 strings of 3.
8 S6-L16-HC batteries in series for 48V.
MS4448PAE
ME-PT-100
MS-PAE
Charging settings (which are adjusted from BTS):
Battery type: custom
Absorb volts: 60
Float: 54
EQ: 62.8
EQ time done: 4h
Absorb Done: 2h
Max Charge Rate: 100%
Final Charge Stage: Multi
I have a generator giving 240V 25A.
After equalization charge I checked the gravities of a few random cells. Most were about 1.230 (uncorrected @ 8C accord to BTS), which I think is undercharged.
Batteries are <6 mo old but I didn't get a generator until recently so they may have been undercharged for a while.
Are these settings about right?
They are all the same as listed on the Rolls website except the EQ voltage. Their range is 62.4-63.6. Should I push mine up?
Thanks in advance,
James
I'm new to the forum and fairly new to the world of solar so would appreciate advice from you seasoned veterans...
We are off-grid with the following set up:
6 LG390N2T panels wired in 2 strings of 3.
8 S6-L16-HC batteries in series for 48V.
MS4448PAE
ME-PT-100
MS-PAE
Charging settings (which are adjusted from BTS):
Battery type: custom
Absorb volts: 60
Float: 54
EQ: 62.8
EQ time done: 4h
Absorb Done: 2h
Max Charge Rate: 100%
Final Charge Stage: Multi
I have a generator giving 240V 25A.
After equalization charge I checked the gravities of a few random cells. Most were about 1.230 (uncorrected @ 8C accord to BTS), which I think is undercharged.
Batteries are <6 mo old but I didn't get a generator until recently so they may have been undercharged for a while.
Are these settings about right?
They are all the same as listed on the Rolls website except the EQ voltage. Their range is 62.4-63.6. Should I push mine up?
Thanks in advance,
James