NEC allows parallel in residential. (If you think I'm wrong, point me to what code section says I'm wrong)
But in practicality - there isn't much need in residential, as parallel wires is at least 1/0, and they must be same electrical characteristics though (same length, cross section, etc) (NEC 310.4 and NEC 310.10)
So why bother with parallel in residential if you're just doing 200A service anyhow. Just get 2/0 and be done. (or 4/0 aluminum)
In general, I'd say if you can meet your needs with 4/0, I would use 4/0 rather than do parallel.
Or in the case of batteries, I would probably look at doing appropriately sized copper bus bars that were
But that's me.
But in practicality - there isn't much need in residential, as parallel wires is at least 1/0, and they must be same electrical characteristics though (same length, cross section, etc) (NEC 310.4 and NEC 310.10)
So why bother with parallel in residential if you're just doing 200A service anyhow. Just get 2/0 and be done. (or 4/0 aluminum)
In general, I'd say if you can meet your needs with 4/0, I would use 4/0 rather than do parallel.
Or in the case of batteries, I would probably look at doing appropriately sized copper bus bars that were
But that's me.