How much water should I add to old AGM battery?
Collapse
X
-
Quit kicking a dead horse and wasting our time. The batteries are Boat Anchors. Geez you do not even know VRLA = AGM. Northstar batteries are made for Telecom and completely useless for cycle service. So stop wasting our time and get rid of them at your local recycle center. -
Ideally a Valve Regulated Lead Acid (VRLA) battery will be charged at a low enough rate that no water will be "boiled off" to a pressure greater than the operating pressure of the valve. Once you have removed (or damaged the integrity of) the valve cap or caps you no longer have VRLA. The pressure is necessary to cause catalytic re-conversion of the elemental oxygen and hydrogen back to water inside each cell.
Maybe this is an older design? Would be interesting to see if the "valves" on the new Northstar batteries are also just thin rubber caps.
Leave a comment:
-
Ideally a Valve Regulated Lead Acid (VRLA) battery will be charged at a low enough rate that no water will be "boiled off" to a pressure greater than the operating pressure of the valve. Once you have removed (or damaged the integrity of) the valve cap or caps you no longer have VRLA. The pressure is necessary to cause catalytic re-conversion of the elemental oxygen and hydrogen back to water inside each cell.Leave a comment:
-
Bear in mind that AGM batteries are 99% saturated with electrolyte. They are designed to be non spill able, in the event that a case gets cracked the electrolyte is supposed to stay suspended in the matting. Adding water seems like it would dilute the electrolyte to a lower specific gravity than a fully charged battery would like to see.Leave a comment:
-
Bear in mind that AGM batteries are 99% saturated with electrolyte. They are designed to be non spill able, in the event that a case gets cracked the electrolyte is supposed to stay suspended in the matting. Adding water seems like it would dilute the electrolyte to a lower specific gravity than a fully charged battery would like to see.Leave a comment:
-
I have a total of 8 batteries so I went ahead and added 30ml of water per cell (that was yesterday). Tried to charge them up a bit (they got about 4kwh) today in a string of 4 batteries. 4 of them showed voltages of 16-19V while charging so those are no good. Kept rotating the bad ones out and of the remaining 4, one of them is giving me 15V, the other 3 seem be charging normally.
Disconnected them now and will test again tomorrow morning after which time I will charge them individually and do further testing.
Don't really know if the water did anything but hey it's worth a try rather than dumping them.
soc2.JPGsoc1.JPGLeave a comment:
-
I have a total of 8 batteries so I went ahead and added 30ml of water per cell (that was yesterday). Tried to charge them up a bit (they got about 4kwh) today in a string of 4 batteries. 4 of them showed voltages of 16-19V while charging so those are no good. Kept rotating the bad ones out and of the remaining 4, one of them is giving me 15V, the other 3 seem be charging normally.
Disconnected them now and will test again tomorrow morning after which time I will charge them individually and do further testing.
Don't really know if the water did anything but hey it's worth a try rather than dumping them.Leave a comment:
-
[QUOTE=sdold;n392744]What does "2 yr warranty/cycle" mean?/QUOTE]
2 years covers manufacturers defects
cycle (Life Cycle) means, lets say in very critical setting ie: Tsunami warning buoys batts must be changed out due to wet, salt, heat, cold and vibration damage . If not thats why they fail and 100s Die.
boy.jpgLast edited by Paul Land; 02-28-2019, 11:06 AM.Leave a comment:
-
These are the batteries I have, they just mention VRLA, nothing about AGM... http://www.northstarbatteri.com/PDF%...r/NSB-AP~1.pdf
Last edited by sdold; 02-27-2019, 02:11 PM.Leave a comment:
-
These are the batteries I have, they just mention VRLA, nothing about AGM... http://www.northstarbatteri.com/PDF%...r/NSB-AP~1.pdfLeave a comment:
-
What does "2 yr warranty/cycle" mean?
I think with batteries in the OP's state, any charge will be an over charge. These are a couple of Liberty LS12-100s that we recently pulled from service, left on a float charger well past their prime. At first glance they seem fine, but if you look closely, you can see what I believe are signs of oxidation (swelling) of the positive plates. These were installed 22 years ago and just pulled out of service.
libertys.jpg .
liberty batt 2.jpgLast edited by sdold; 02-27-2019, 01:53 PM.Leave a comment:
-
Mike, you will find these Batts way up on-top that Mt, behind your house and they have 2 yr warranty/cycle when there new. they are a zero touch zero maint, back-up batts.Leave a comment:
-
Leave a comment:
-
It's still useful. You just have to find a system that runs on 10 volts.Leave a comment:
-
AGM batteries are susceptible to sulfation, just not as readily as FLA. Loss of water (only) from the electrolyte will cause loss of capacity but NOT reduced open circuit voltage after full charge. Your voltages and lack of response to charging are most likely the result of irreversible sulfation, not overboiling.
As such, the door stop idea has merit, but the value will be greater as lead scrap. Any AGM battery over five years old, used or unused, is suspect.
However, I do not know of any AGM (sealed) batteries to which you can add water without drilling or using a hypodermic and then resealing to hold gas pressure.
I may try looking the battery up.
Old FLA, especially ones that have been sitting uncharged are unrecoverable because of sulfation. Door stop recommendation still applies.
IF (and a big if) electrolyte was actually spilled instead of boiled off, adding electrolyte rather than water might get you some very limited use.
If the tops of the plates were uncovered for any length of time, the battery will have lost capacity.
OK, that part number is indeed sealed AGM, so there will be no way to add water, period. That is why AGM batteries should never see an Equalize cycle with a high enough voltage and current to cause venting.
The batteries I have do have venting holes and upon taking the cover off there are 6 holes with thin rubber caps on them.
IMG_20190227_094808_1.png
IMG_20190227_094504.png
IMG_20190227_094520.pngLeave a comment:
Leave a comment: