Trojan recommends between 10 - 13% of the C20 rating which for my L16RE-A batteries is between 32.50 and 42.25 DC charging amps. Using my 5kw diesel generator I can get right at 42.25 amps by setting my XW5545 inverter/charger to 29% charge rate. If I set my charge rate to 100% my batteries will see 75 to 85 DC amps when bulk charging at about 80% SOC. I haven't let them charge at these high rates for more than ten minutes or so but the battery temps didn't go above 55 degrees Fahrenheit. I rarely have to use a generator in the summer and would only consider these higher rates when it is cold out, assuming I'm not shortening the life of my batteries.
The RV boondockers believe in high charge rates to reduce generator run time.
So my question: is it OK o bulk charge at these high current rates as long as I don't let the batteries get above 55 to 60 degrees Fahrenheit? Is there any benefit? I have read that deep cycle batteries actually charge more efficiently at lower current. Just trying to maximize fuel efficiency from the diesel generator.
I called Trojan and the tech told me I could go up to 20% as long as the batteries don't heat up. That would be 65 amps.
The RV boondockers believe in high charge rates to reduce generator run time.
So my question: is it OK o bulk charge at these high current rates as long as I don't let the batteries get above 55 to 60 degrees Fahrenheit? Is there any benefit? I have read that deep cycle batteries actually charge more efficiently at lower current. Just trying to maximize fuel efficiency from the diesel generator.
I called Trojan and the tech told me I could go up to 20% as long as the batteries don't heat up. That would be 65 amps.