I was sold these batteries by a local forklift service center as "Trojan Black Box". They do not have trojan badges on them and I was told they are 210ah 6v flooded batteries. I have 4 batteries wired in series-parallel giving me a 420Ah 12v bank for use as a house battery on a camper.
I have had them in service for ~3 mo and I have started to notice a lot of Voltage Sag. During these 3 months, the batteries have been charged by solar panels at 14.4v and by the alternator to a similar voltage while driving. What recently got my attention was that I saw the battery voltage drop to ~12v under a small 20A load (C/20) shortly after coming off being fully charged. I thought that was far too dramatic of a drop and started investigating.
I increased the charge voltage to 14.8v to try and make sure they were getting a full charge. Here is a picture with the up to date hydrometer numbers and voltages. the lowest is a 1.256 and the highest is a 1.276. They are very consistent between cells of the same battery. Voltages are 7.5v &7.3v for one series string and 7.6v and 7.2v on the other string.
When doing my hydrometer readings I also noted that one series string has significantly more black build up on the underside of the caps. The other string has hardly any. Not sure if this gives any clues as to what may be happening during charge or discharge.
I have also noticed when bubbling at 14.8v that I get very large bubbles. It is not a constant fizzing sound but more like a big bubble just got released and rushed to the top of the battery. I have also had a small amount of electrolyte come out of 2 battery cells during this charging. It is almost always from the same cells which are on the string with the black deposits on the caps, The fluid level appears to be correct at just below the well.
Hoping you all can help enlighten me on what has happened and hopefully reclaim some of my capacity.
Please let me know what other investigation I can do to help troubleshoot!
Thanks,
Matt
I have had them in service for ~3 mo and I have started to notice a lot of Voltage Sag. During these 3 months, the batteries have been charged by solar panels at 14.4v and by the alternator to a similar voltage while driving. What recently got my attention was that I saw the battery voltage drop to ~12v under a small 20A load (C/20) shortly after coming off being fully charged. I thought that was far too dramatic of a drop and started investigating.
I increased the charge voltage to 14.8v to try and make sure they were getting a full charge. Here is a picture with the up to date hydrometer numbers and voltages. the lowest is a 1.256 and the highest is a 1.276. They are very consistent between cells of the same battery. Voltages are 7.5v &7.3v for one series string and 7.6v and 7.2v on the other string.
When doing my hydrometer readings I also noted that one series string has significantly more black build up on the underside of the caps. The other string has hardly any. Not sure if this gives any clues as to what may be happening during charge or discharge.
I have also noticed when bubbling at 14.8v that I get very large bubbles. It is not a constant fizzing sound but more like a big bubble just got released and rushed to the top of the battery. I have also had a small amount of electrolyte come out of 2 battery cells during this charging. It is almost always from the same cells which are on the string with the black deposits on the caps, The fluid level appears to be correct at just below the well.
Hoping you all can help enlighten me on what has happened and hopefully reclaim some of my capacity.
Please let me know what other investigation I can do to help troubleshoot!
Thanks,
Matt