have two Crown CR-GC150 12v FLA deep cycle 150AH each, connected in parallel so 300 AH available. Run them down with a 4.5amp load, should get about 2000 watts out of the set at 50%soc, but only getting 1200-1500. Less than a year old, never below 50%soc, never not immediately recharged after a 50%soc run down. At 12.2v at rest = 50% soc, SG @ 1200. Put a 100 amp load on them and voltage sags immediately to 11.2v.
When I recharge them with Xantrex inverter/charger at 35amps at completion of charge cycle, battery voltage ok, but SG at 1175. Hit with a 2 hour 15.2v 15amp equalization cycle, and I can get SG to 1250. Spec is 1275, which I can get them there with their spec'd equalization cycle of 16.2v for 4 hours at 15amps. (spec for one battery is 5amps, so with two i push to 15amps)
But next 4.5 amp load/recharge cycle, they only get back to SG 1175...
Does this sound like a battery issue or a charger issue?
When I recharge them with Xantrex inverter/charger at 35amps at completion of charge cycle, battery voltage ok, but SG at 1175. Hit with a 2 hour 15.2v 15amp equalization cycle, and I can get SG to 1250. Spec is 1275, which I can get them there with their spec'd equalization cycle of 16.2v for 4 hours at 15amps. (spec for one battery is 5amps, so with two i push to 15amps)
But next 4.5 amp load/recharge cycle, they only get back to SG 1175...
Does this sound like a battery issue or a charger issue?