  • Mike90250
    replied
    Originally posted by NEOH
    Then, why not opposite ends of the bus bar ...
    usually makes complex cable issues, I like more symmetrical cables.

    Leave a comment:


  • NEOH
    replied
    Originally posted by dapago

    Will do it as you suggest. My problem is to find the busbar here. Have been calling many electrical supplier AND the very few solar provider, nobody has busbar
    Is cadmium-plated solid copper OK ?

    example: Something like this ...

    https://www.ebay.com/itm/Solid-Coppe...0AAOSwDNdV3eqG

    Leave a comment:


  • Sunking
    replied
    Originally posted by NEOH

    Can the OP add a DC Rated Fuse in series with each string ?
    Yes but it needs more OCPD/ As you noted one OCPD on each battery, but there also needs to be OCPD looking at the CC and Load on the buss feeders.

    Leave a comment:


  • dapago
    replied
    Originally posted by Sunking

    Does not compute. Busbars are not rated in AH, the are rated in AMPS. The busbar current ratings (Amps) must be equal to or greater than the load imposed on it. If you have at least 1/8 inch thick copper 1 inch wide busbars will exceed anything you can throw at it as it will be rated at least at 200 amps.

    FWIW the bus bars are the least of your concerns, or perhaps mine. What I want to know is just how you plan to integrate Over Current Devices using bus bars.
    My mistake sorry.

    will try to find 200 amps busbar or may have to order them in the US. Was thinking of using earth bar but apparently (true?) I have been told that they are only brass coated (?)
    Last edited by dapago; 10-24-2017, 12:44 PM.

    Leave a comment:


  • dapago
    replied
    Originally posted by NEOH

    Then, why not opposite ends of the bus bar,
    Inverter (+) @ top of bus bar, near string #1's connection
    Inverter (-) @ bottom of bus bar, near string #3's connection

    Same with CC's
    Will do it as you suggest. My problem is to find the busbar here. Have been calling many electrical supplier AND the very few solar provider, nobody has busbar

    F169EE73-3AC7-4477-8FB7-7A9159E2481F.jpeg
    Last edited by dapago; 10-24-2017, 12:54 PM.

    Leave a comment:


  • NEOH
    replied
    Originally posted by Sunking

    Does not compute. Busbars are not rated in AH, the are rated in AMPS. The busbar current ratings (Amps) must be equal to or greater than the load imposed on it. If you have at least 1/8 inch thick copper 1 inch wide busbars will exceed anything you can throw at it as it will be rated at least at 200 amps.

    FWIW the bus bars are the least of your concerns, or perhaps mine. What I want to know is just how you plan to integrate Over Current Devices using bus bars.
    Can the OP add a DC Rated Fuse in series with each string ?

    Leave a comment:


  • NEOH
    replied
    Originally posted by Mike90250

    I'd size it for 2x the surge rating of your inverter. AND i'd feed it from the center of the bussbar, not the end

    if the inverter can draw 250A at surge, i'd size the bussbar to 500a
    Then, why not opposite ends of the bus bar,
    Inverter (+) @ top of bus bar, near string #1's connection
    Inverter (-) @ bottom of bus bar, near string #3's connection

    Same with CC's

    Leave a comment:


  • Mike90250
    replied
    Originally posted by dapago
    An other question. What Ah is needed for the busbar for my bank?
    I'd size it for 2x the surge rating of your inverter. AND i'd feed it from the center of the bussbar, not the end

    if the inverter can draw 250A at surge, i'd size the bussbar to 500a

    Leave a comment:


  • Sunking
    replied
    Originally posted by dapago
    An other question. What Ah is needed for the busbar for my bank?
    Does not compute. Busbars are not rated in AH, the are rated in AMPS. The busbar current ratings (Amps) must be equal to or greater than the load imposed on it. If you have at least 1/8 inch thick copper 1 inch wide busbars will exceed anything you can throw at it as it will be rated at least at 200 amps.

    FWIW the bus bars are the least of your concerns, or perhaps mine. What I want to know is just how you plan to integrate Over Current Devices using bus bars.
    Last edited by Sunking; 10-23-2017, 11:40 PM.

    Leave a comment:


  • Sunking
    replied
    Originally posted by dapago
    Just need to know if that is correct and if each batts will be well balanced.
    cant afford to damage my batts or have unbalanced batts.
    Yes.

    Leave a comment:


  • dapago
    replied
    An other question. What Ah is needed for the busbar for my bank?

    Leave a comment:


  • dapago
    replied
    017B5036-FA62-453B-868C-237A7D24FD8C.jpeg



    i have made a little diagram. Just need to know if that is correct and if each batts will be well balanced.
    cant afford to damage my batts or have unbalanced batts.
    Last edited by dapago; 10-23-2017, 09:39 PM.

    Leave a comment:


  • dapago
    replied
    Originally posted by inetdog

    For lead-acid batteries you do NOT want to add the cross connections (dotted lines). The batteries and strings will be better equalized if you do not use them.
    For lithium chemistry batteries, which do not tolerate overcharging some batteries in a string to get full charge on others, you would want to use the cross connections.
    Thanks a lot for your inputs!!! Really appreciate it.

    Leave a comment:


  • Sunking
    replied
    Originally posted by dapago

    So I don
    You can connect Pb batteries as show below (Alternative) IF THE CELLS ARE 2 VOLTS. They cannot be 4, 6, 8, 12, 24, or 36 volt Pb batteries which is shown Conventional.

    Leave a comment:


  • inetdog
    replied
    Originally posted by dapago
    My answer is not showing On my iPad
    will open a new message.
    i was asking that if the dot lines are not necessary, will the bank be well balanced?
    if not, can we use method 4 and if so what will be the diagram?
    sorry to bother you again
    For lead-acid batteries you do NOT want to add the cross connections (dotted lines). The batteries and strings will be better equalized if you do not use them.
    For lithium chemistry batteries, which do not tolerate overcharging some batteries in a string to get full charge on others, you would want to use the cross connections.

    Leave a comment: