So the thread I started asking about LBCO for my inverter at times seemed to deviate, and so I wanted to start a different thread specifically about my new battery bank. I am needing help understanding various characteristics and what is considered normal battery behavior and what might be a problem with the batteries or the system.
Here is the set up:
- 4 New Trojan L16H-AC 435Ah batteries in series at 24v.
- Schneider Conext SW 4024 Inverter / Charger
- 6 Selectable Circuits coming in from the inverter with various loads.
The most watts I can load up on the entire system with everything I can find to run on every circuit is less than 2000 watts (excluding fridge and pump start up surges that last 30 secs or less).
Here are the Conditions in Question: When I am running this 24v system WITHOUT the AC in Support at between 500 and 600 watts on the system running on the batteries only, my 4 fully charge Trojans voltage will begin to drop rather quickly. At 600 watts, that 25.7 voltage starts to drop right before my eyes down to 25.2v and if the pump kicks on taking the system to 1300 watts for 30 seconds the batteries will Sag to 24.6v at the that 1300 watt load. When the startup surge relaxes and things setting down to about 600-800 watts with the pump running (usually less than a 30 seconds) the battery voltage be about 25v or just below.
But during that surge of start up, the SW 4024 inverter gets a fault that says "DC Under Voltage Fault" (which means according to the manual the DC voltage at the inverter terminals dropped below LBCO for 10 seconds). I have the LBCO set to 24v and I have a delay on LBCO for 30 seconds ... so the Inverter does not shut off. But the inverter records a momentary volt drop below 24v. I do not see it on the display because it happens so fast. But in the surge for 15-25 seconds I am seeing a voltage of 24.5 +/-
When the pump kicks off, and the load goes to 200-300 watts, the battery voltage goes up to about 25.2v and as soon as I turn off the inverter and return the system to an AC Line in for supply, (that is the batteries are just sitting ideal) the battery voltage returns to 25.4 to 25.6v +/- with in a minute or two .
Here are the questions:
Help me make sense of this. Is this Typical and I am undersized ... or do I possibly have a problem with the system or batteries? Any comments or suggestions about this would be appreciated. Thanks for your time.
Here is the set up:
- 4 New Trojan L16H-AC 435Ah batteries in series at 24v.
- Fully charged at 25.7v
- Connected to each other with 4/0 cable that is 9" long each connection x3 cables ... and to the inverter from the battery bank with 4/0 cable that is 9 feet long.
- All the individual batteries at open circuit are balanced with in a few 1/100th's of a volt.
- Schneider Conext SW 4024 Inverter / Charger
- AC out on #8 with a 30 amp breaker
- AC in on #8 with a 30 amp breaker (for back up support AC - which does not seem to be working correctly so I am working with Schneider about that - and charger operation)
- 6 Selectable Circuits coming in from the inverter with various loads.
1. Fridge 20amp breaker (runs between 100-300 watts using 2350 Wh's / day)
2. Well pump 20 amp breaker (Start up of 800w / running at 735w using 550 Wh's / day. )
2. Well pump 20 amp breaker (Start up of 800w / running at 735w using 550 Wh's / day. )
(All other loads below less than 600 Wh's / day)
3. LED lights 15 amp breaker
4. LED lights 15 amp breaker
5. Various receptacles 15 amp breaker (most not being used)
6. LED light and receptacles 15 amp breaker (not in use or turned on on the battery)
4. LED lights 15 amp breaker
5. Various receptacles 15 amp breaker (most not being used)
6. LED light and receptacles 15 amp breaker (not in use or turned on on the battery)
The most watts I can load up on the entire system with everything I can find to run on every circuit is less than 2000 watts (excluding fridge and pump start up surges that last 30 secs or less).
Here are the Conditions in Question: When I am running this 24v system WITHOUT the AC in Support at between 500 and 600 watts on the system running on the batteries only, my 4 fully charge Trojans voltage will begin to drop rather quickly. At 600 watts, that 25.7 voltage starts to drop right before my eyes down to 25.2v and if the pump kicks on taking the system to 1300 watts for 30 seconds the batteries will Sag to 24.6v at the that 1300 watt load. When the startup surge relaxes and things setting down to about 600-800 watts with the pump running (usually less than a 30 seconds) the battery voltage be about 25v or just below.
But during that surge of start up, the SW 4024 inverter gets a fault that says "DC Under Voltage Fault" (which means according to the manual the DC voltage at the inverter terminals dropped below LBCO for 10 seconds). I have the LBCO set to 24v and I have a delay on LBCO for 30 seconds ... so the Inverter does not shut off. But the inverter records a momentary volt drop below 24v. I do not see it on the display because it happens so fast. But in the surge for 15-25 seconds I am seeing a voltage of 24.5 +/-
When the pump kicks off, and the load goes to 200-300 watts, the battery voltage goes up to about 25.2v and as soon as I turn off the inverter and return the system to an AC Line in for supply, (that is the batteries are just sitting ideal) the battery voltage returns to 25.4 to 25.6v +/- with in a minute or two .
Here are the questions:
- Given internal resistance, would this be normal behavior for New Trojan L16H-AC 435Ah batteries x 4 in series for 24v?
- Am I correct in assuming that the 435Ah 24v battery bank should be good for 10.4 kw / 2 (50%) = 5.2 kw of storage?
- My total daily load that I calculated is 3400 watts? Should I be able to go for 24 hours with my existing battery bank? (3400/24v = 142 Ah)
- But how much of the time you can run on battery is effected by heavy loads, like start up loads and extended heavy run loads? Say 1300-1800 watts for 10 to 15 minutes 2 times a day
- How long could I expect the system to operate under battery power alone if I am drawing an average of 200 - 300 watts per hour? (at 300 watts I am figuring I could run for 17 hours with out any charge input before I hit the 5.2 Kw of storage in the battery - is that correct?)
- Does all this sound typical ... Or Do I need a larger battery bank to handle this load for 1 day of autonomy and especially the the larger start up loads and brief run times even if not very long because the voltage will sag? ( say 8 L16s at 870Ah)
Help me make sense of this. Is this Typical and I am undersized ... or do I possibly have a problem with the system or batteries? Any comments or suggestions about this would be appreciated. Thanks for your time.