We are running (6) almost new 50AHr Universal UB12500 batteries in parallel for a ham radio application. The batteries are all 5.5 mOhms and range from 470 to 500 CCA after a night’s rest. The batteries seem to vary between 13.0 to 12.65V after rest. The battery bank is charged using a Morningstar MPPT controller providing about 14A under full sun.
A draw of 15 amps draws the batteries to under 12.0 volts after about 5 hours. However, a 25 amp draw on the charged batteries brings the runtime voltage down below 12.0V after 90 minutes. With a total capacity of 300 AHrs, It would seem that the bank should easily handle 3-4 hours of 25A and still be over 12.0 volts. The radio equipment must be supplied at least 12.0 volts to reliably operate.
Are the batteries handling the 25A load properly? Is there a way to maintain a 25A draw at or above 12.0 volts for a longer percentage of the battery rated capacity? Would it significantly lengthen the operating time if the batteries were moved into 3 parallel sets of 2 batteries at 24V, with a 24V to 12V step-down converter?
Any assistance is appreciated, Ron
A draw of 15 amps draws the batteries to under 12.0 volts after about 5 hours. However, a 25 amp draw on the charged batteries brings the runtime voltage down below 12.0V after 90 minutes. With a total capacity of 300 AHrs, It would seem that the bank should easily handle 3-4 hours of 25A and still be over 12.0 volts. The radio equipment must be supplied at least 12.0 volts to reliably operate.
Are the batteries handling the 25A load properly? Is there a way to maintain a 25A draw at or above 12.0 volts for a longer percentage of the battery rated capacity? Would it significantly lengthen the operating time if the batteries were moved into 3 parallel sets of 2 batteries at 24V, with a 24V to 12V step-down converter?
Any assistance is appreciated, Ron