When using say two 6v 200ah golf cart batteries in a 12v setup you would parallel them and get 200ah. If you had a 24v system then two of the same 6v 200ah batteris in series would make 400ah? If that's the case then you'd spend half the $ on a 24v system and you can use a charge controller that can interface 12v solar panels with a 24v battery bank right? Why go 12v then? (Besides the use of 12v DC electronics)
12v vs 24v battery bank amp hours
Collapse
X
-
-
to use 6v batteries in a 12V setup, you SERIES them, battery_wire_diag.jpg (the top row of batteries in the sketch are in series)
Batteries (pr PV panels) in SERIES, increases Volts
Parallel, increases AMPS. Since Volts x Amps = Watts, either method still produces the exact same watts, but higher voltages have less losses, and a few % more efficiency.Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister -
to use 6v batteries in a 12V setup, you SERIES them, [ATTACH=CONFIG]2070[/ATTACH] (the top row of batteries in the sketch are in series)
Batteries (pr PV panels) in SERIES, increases Volts
Parallel, increases AMPS. Since Volts x Amps = Watts, either method still produces the exact same watts, but higher voltages have less losses, and a few % more efficiency.Comment
-
For the same amount of power (volts x amps if you leave out power factor which is an AC thing) the current is lower when you use a higher voltage. 12 volts time ten amps gives 120 watts, while 120 volts times 1 amp gives the same power.
Since the power loss in a given size wire is lower when the current is lower, higher voltages translate to lower losses.SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment
-
So if I decided to go with a 24V system over 12V system and using the same SIZE bank of say 440ah..
Running a 2000 watt AC inverter (24v rated).. will I use less AH then the same setup at 12V rated (12v bank and 12v inverter and same 2000 watt inverter)??
I know I can use lighter wire then the 3/000 I have for the 12V bank.. but if the DRAW is the same for the 2000 watt inverter (say 55amps) is there any advantage other then lighter gauge wiring??
I also know I can use smaller breakers on the bank if I go with 24v..
I haven't totally decided if I am going 12 or 24 yet (my controller can do both and I can get 1 more panel and get a total PV of 870 if I want to go 24).. which is better I think than 725 @ 12V that I currently have planned for my 5 panels..
My controller limit (Morningstar TS45 (PWM)) is 5 panels @ 145 if I go 12V in parallel (725w).
if I step to 24v I can go with 3 parallel strings of 2 (series) and be at the 870 watts of PV..
I was leaning toward 12V for the less expensive 2000w inverters for 12v.. (the 24V ones of same 2K rating are like $600+)..
I plan on running an Air Conditioner for 2 hours a day rated at about 55 amps / hour..
So if the 24V system would give me a clear advantage (drawing less out of the same 24v bank) then I would consider heavily going with 24v and biting the bullet on the higher priced 2000w 24v inverter.1160 watts, Midnite 150 , Xantrex SW2000Comment
-
First off a 12 volt 440 AH battery bank, and a 24 volt 440 AH bank are not equal in capacity, there is a 100% difference. 12 volts x 440 AH = 5280 watt hours. A 24 volt x 440 AH = 10560 watt hours.MSEE, PEComment
-
So I would be pulling 22 1/2 amps from a 24v inverter and bank??1160 watts, Midnite 150 , Xantrex SW2000Comment
-
Assuming the same battery bank wiring you'd actually pull a little less. At 24V you will start with half the current, thus you get 1/4 of the losses that you would get at 12 volts. (Losses=I^2R in watts, so 2x current draw = 4x losses.) That means the inverter will not have to draw a little more current to counteract the additional losses in the wiring. Which is one of many reasons that higher voltages are in general better than lower voltages.Comment
-
Assuming the same battery bank wiring you'd actually pull a little less. At 24V you will start with half the current, thus you get 1/4 of the losses that you would get at 12 volts. (Losses=I^2R in watts, so 2x current draw = 4x losses.) That means the inverter will not have to draw a little more current to counteract the additional losses in the wiring. Which is one of many reasons that higher voltages are in general better than lower voltages.1160 watts, Midnite 150 , Xantrex SW2000Comment
-
Comment
-
Comment
-
for your air conditioning.
If your panels can produce as much power as the AC consumes, then you are in heaven, you are not stressing the batteries at all. Ignoring the brief blips as clouds shade the panels (that's when the batteries stabilize the power flow) if your bank is charged at noon, and you fire up the AC, you can run it as long as your panels produce the same power, maybe till 3pm, and you won't dent the battery bank.
But unless you have one of the low power, Mini-Split systems, most 12V rigs will have a hard time starting up the AC compressor. 24 or 48V systems have much more starting power, when my well pump kicks on, there is no flicker in the lights at all.Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
for your air conditioning.
If your panels can produce as much power as the AC consumes, then you are in heaven, you are not stressing the batteries at all. Ignoring the brief blips as clouds shade the panels (that's when the batteries stabilize the power flow) if your bank is charged at noon, and you fire up the AC, you can run it as long as your panels produce the same power, maybe till 3pm, and you won't dent the battery bank.
But unless you have one of the low power, Mini-Split systems, most 12V rigs will have a hard time starting up the AC compressor. 24 or 48V systems have much more starting power, when my well pump kicks on, there is no flicker in the lights at all.
I was planning on a Xantrex Pro SW 2000 inverter.. I have 3/0 wire here and a battery switch..1160 watts, Midnite 150 , Xantrex SW2000Comment
-
OK I hope you are aware a solar panel does not generate its rated power. At best around 85 to 90% of its rated power. Second it will only generate that 85 to 90% only for about 1 to 2 hour per day around Solar Noon, and that is only if the skies are crystal clear.MSEE, PEComment
-
1160 watts, Midnite 150 , Xantrex SW2000Comment