I've created an off grid Solar system which powers select loads.
The solar Panel's are connected to a Charge controller, which is connected to a 24v, 450ah battery bank. An inverter is connected directly to the battery bank, and a relay is on the load output on the charge controller, so when the charge controller goes into low voltage disconnect, the inverter shuts off. There's an automatic transfer switch that puts the load back on the Grid once in LVD. There's an online double conversion UPS, between the inverter and the load. This setup seems to work great. When the Inverter cut's out the UPS steps in for the few seconds for the relay to switch.
The charge controller LVD is set to 22.1v. The average load is 300 - 400 watts. I've noticed under this load, after the batteries have normalized for a couple hours, they're at 24.48v or about 60%. Can/Should I try lowering the LVD? so it discharges down to 30% or 40%? I'm only seeing about 1.5 - 2.0 KWH of power drained from the battery until LVD.
Thanks in advance.
The solar Panel's are connected to a Charge controller, which is connected to a 24v, 450ah battery bank. An inverter is connected directly to the battery bank, and a relay is on the load output on the charge controller, so when the charge controller goes into low voltage disconnect, the inverter shuts off. There's an automatic transfer switch that puts the load back on the Grid once in LVD. There's an online double conversion UPS, between the inverter and the load. This setup seems to work great. When the Inverter cut's out the UPS steps in for the few seconds for the relay to switch.
The charge controller LVD is set to 22.1v. The average load is 300 - 400 watts. I've noticed under this load, after the batteries have normalized for a couple hours, they're at 24.48v or about 60%. Can/Should I try lowering the LVD? so it discharges down to 30% or 40%? I'm only seeing about 1.5 - 2.0 KWH of power drained from the battery until LVD.
Thanks in advance.
Comment