Battery interconnect Cable Size.
  • Zardiw
    • Nov 2015
    • 77
    Hey Guys...I'm making a battery bank using 12 2V L16's to make 24V.........my question is what size would be good to interconnect the batteries.
    Inverter is 4000Watt, and down the road will probably add another 4000W inverter....so draw could get pretty high
    Gonna use 4/0 to come off the bank to the inverter, but was wondering what size I need between the batteries.......
    Thanks!
    z
    Whoa. 8Kw of inverters. You NEED to seriously change plans and go for 48V. And an energy diet.
      Now that is some funny stuff coming from a guy who makes a video and claims to be an Expert on the idiots bible You Tube "R" Screwed. You have no clue just how dangerous that is and the batteries cannot handle that large of an Inverter. Your life and property not mine. glad you do not live anywhere close to me.
      But I will answer your question since you have no clue what you are doing. 4000 watts on a 24 volt battery will draw 200 amps, more than a house would draw. To do that without making a fire bomb, which is what you are making, would require a minimum 4/0 AWG which you stand no chance of terminating correctly without a 16-ton hydraulic compression tool and training. Not to mention the Inverter Input Terminals are not likely capable of handling 200 amps or facilitating a lug large enough to handle the current or mechanical stress.
      Bottom line Inter-cell cables must be as large or larger then the Feeder to the Inverter and a 200 line minimum requirement is 4 AWG or larger if any distance is involved. Hope you have a 3000 to 4000 wat panel system with two very expensive 60 to 80 amp charge controllers. Bet you did not know that either You Tube Expert.
      • Zardiw
        • Nov 2015
        • 77
        Wow......You're absolutely right. I'm gonna convert to 48V........that will solve a lot of problems...Will let me hook up twice the panels to one Morningstar MPPT60 and knock down the amperage and cable sizes.......Thank You!!!
        • Zardiw
          • Nov 2015
          • 77
          Currently using 4/0 cables on one battery string.....but I'm gonna hook up another string of 12 2V L16's. Going to upgrade to 48V, which will knock down the cable size requirements. Thanks for the info on the cable size. Will have to buy a Magnum 48V inverter and sell my 24V one on EBay down the road. For now will hook up the other string and stay at 24V. Have enough room in my battery box for another 12 L16's. So when I go to 48V will have 24 2V L16's on one string and 8 6V L16's on the other string.
          z
            • 5208
            At some point bus bars tend to replace big wire. Bruce Roe
            • gbynum
              • Dec 2014
              • 65
              12 older cells, 12 newer cells ... be wary. Parallel is not good, parallel of other than identical is bad.