The specific voltage and losses will vary between brands of controllers, battery voltage requirements and length of PV HVDC cable run.
Midnight publishes 1.3x battery voltage, however My opinion is that would be the Bulk/Absorb Voltage, since that's where the most power is required. Float and EQ don't consume a lot of current.
I have a classic 200, running 180V into it to charge a "48V" bank. With my array and fitting additional wires into conduit, I had to go with higher voltage to get lower amps, to use thinner wire. With a 2Kw array it runs fairly hot, however, ALL classics run fairly hot, they have 2 stages of fans, and the turbo fan speed is quite loud and annoying.
Midnight publishes 1.3x battery voltage, however My opinion is that would be the Bulk/Absorb Voltage, since that's where the most power is required. Float and EQ don't consume a lot of current.
I have a classic 200, running 180V into it to charge a "48V" bank. With my array and fitting additional wires into conduit, I had to go with higher voltage to get lower amps, to use thinner wire. With a 2Kw array it runs fairly hot, however, ALL classics run fairly hot, they have 2 stages of fans, and the turbo fan speed is quite loud and annoying.