I never said you cannot parallel them, I said you WOULD NOT WANT to parallel them. Big difference. If you parallel any modular battery (more than 1-cell in series), does not matter what type, you are going to significantly shorten cycle life. Proven fact Jack.
There is not one single LFP battery or any battery with 10,000 cycles in existence.
20 - 30 year battery. 50 -60% cycles. Now that is some funny stuff, I don't care who you are. One cloudy day and you go dark.
[Moderator note - removed irrelevant content]
Battery Comparison for 48V off grid system
Collapse
X
-
Last edited by sensij; 01-13-2018, 12:46 PM. -
"PHI SMART-TECH BATTERIES ARE DESIGNED FOR PARALLEL OPERATION ONLY - DO NOT ARRANGE IN SERIES FOR INCREASED VOLTAGE"
Next in line is with AGM you can discharge them deeper than FLA batteries. You can take them down as far as 80% DOD which is exactly what a LFP battery can do. But you should never allow that to happen with either battery. You want to limit discharge to 20 to 30% per day on any battery type.
Both the AGM and LFP have roughly the same cycle life and usable capacity,..
Here is the deal the AGM and LFP battery warranty is 2 years.
Simon
Off grid 24V system, 6x190W Solar Panels, 32x90ah Winston LiFeYPO4 batteries installed April 2013
BMS - Homemade Battery logger github.com/simat/BatteryMonitor/wiki
Latronics 4kW Inverter, homemade MPPT controller
Leave a comment:
-
Hey Sunking, thanks for the response! That was a pretty easy calculation!
On the Simplifi battery we were looking at the 48V version. Their specifications section shows the 48V with 67 AH and 3440 Watt Hours - which I guess the real # is 3216 Watt hours based off the calculation you provided. If I had three of those in series is that as simple as 3 x 3216 = 9648 watt hours?
If so the AGM's at 50% DOD would give me a usable 19,920 watt hours which is still slightly more than double with taking the Simplifi batteries to 100% DOD.....
Am I even close???
Next in line is with AGM you can discharge them deeper than FLA batteries. You can take them down as far as 80% DOD which is exactly what a LFP battery can do. But you should never allow that to happen with either battery. You want to limit discharge to 20 to 30% per day on any battery type.
As for the error you discovered in capacity, the Simplifi nominal battery voltage is slightly higher than the AGM lead acid. Lead Acid nominal is 48 volts and the LFP is 51ish volts. Try that and you get the 3440 wh. You are correct the watt hours add so if you had 3 x 3216 = 9648 wh.
None of the above is all that important. What is important is what you wallet thinks as it is the boss of everything. Your wallet would fire you if you used the LFP battery. Both the AGM and LFP have roughly the same cycle life and usable capacity, and here is what your wallet wants to know. Your wallet demands to know what is the $/wh cost. To figure that out take the cost of one unit, and calculate the $/wh cost. With just a quick search 1 unit of the Full River 6-volt 415 AH battery cost $510 each and yields 2490 watt hours. So $510/2490 = $ 0.20 - wh. I also found the 48 volt 3440 wh Simplifi 48 volt 67 AH unit for $3675, so $3675 / 3400 wh = $1.08-wh.
Now I do not know what your wallet would say about that, but mine says you would be a damn fool to buy the LFP battery paying 500% more. What does your wallet say about that? It is a No-Brainer decision when you know the facts. Let your wallet do your thinking and not the piece of meat between your ears or legs.
Do I have your attention yet? If so what about using say a Rolls S-550 a FLA 6-volt 428 AH battery. Unit cost is roughly $335. Here is why you should consider them, your wallet. Here is the deal the AGM and LFP battery warranty is 2 years. The Rolls is 7-years which means they should last at least 3 times longer. If you do the life cycle calculations using 25% DOD per day, the wh delivered cost of AGM is 400% higher than FLA, and LFP is 1200% higher than FLA. What does your wallet say about that?
Look AGM has applications in solar, but you need to justify the higher cost. To do that requires 1 of the following conditions to be met:- Extreme cold environment of -40 degrees. At those temps eliminate LFP period.
- Unusual mounting orientation like on their side.
- Spills cannot be tolerated like on an aircraft which is why AGM was invented.
- Very high charge and discharge rates.
Last edited by Sunking; 01-12-2018, 01:07 PM.Leave a comment:
-
In addition to the Simplifi, another LiFePO4 possibility is with the new Discover 48 V 6.6 kWhr Canbus capable batteries with integral BMS (Top balancing ???). They are designed to report S.O.C. to Schneider Conext and SMA systems and auto generator start which provides added levels of operating convenience and safety. They also provide battery monitors that link to the Canbus that display SOC.
I have no idea if they are more economically attractive than the Simpli Phi but from what I have seen so far Discover is an impressive company, and they are local to us here in BC!
I'm still leaning towards old tech 24 times 2 V tubular FLA cells (with a simple wave powered flapper valve column off the dock as an airlift pump for anti-acid stratification ??) for our island home's 48 V battery bank / XW system. We are also pondering FLA vs AGM vs LiFePO4, but perhaps things are changing faster than we all realize ....
42-48-6650 Advanced Energy System Battery Specifications:
Case Study:
Anyone else familiar with these new batteries?
- SolarislandersLeave a comment:
-
Hey Sunking, thanks for the response! That was a pretty easy calculation!
On the Simplifi battery we were looking at the 48V version. Their specifications section shows the 48V with 67 AH and 3440 Watt Hours - which I guess the real # is 3216 Watt hours based off the calculation you provided. If I had three of those in series is that as simple as 3 x 3216 = 9648 watt hours?
If so the AGM's at 50% DOD would give me a usable 19,920 watt hours which is still slightly more than double with taking the Simplifi batteries to 100% DOD.....
Am I even close???Last edited by cgofish; 01-10-2018, 10:50 PM.Leave a comment:
-
Well this sis easy peazy and a slam dunk.
Capacity of any battery is Voltage x AH = Watt Hours
So the AGM is 48 volts x 830 AH = 39,840 watt hours or 39.8 kWh
The other is a rip off you should stay far away from. 24 volts x 134 AH = 3216 watt hours or 3.2 kWh. You cannot use 3 of them at 24 volts, only in groups of two. You would have to have 10 of the batteries to equal the AGM.
No contest.Leave a comment:
-
Battery Comparison for 48V off grid system
Hi all, I was wondering if someone could help me with a watt hour calculation on these two proposed sets of batteries:
Original proposed set up was 16 Fullriver DC400-6 AGM Sealed 6V 415Ah Batteries. Two stings of 8 for the set up.
Optional proposed set up is using Simpliphi PHI 3.4 48V battey. As I understand it 3 total.
I have a good general understanding of the differences in the battery chemistry and different DOD recommendation for each type. What I'm having a hard time calculating with any level of confidence is the usable capacity of both set ups. If someone can point me in the right direction to figure that out I'd appreciate it.
Any other comments or recommendations are always welcome.
Reference links to the two batteries:
https://www.wholesalesolar.com/cms/f...4017212128.pdf
Whether looking for backup power, adding capacity with solar+storage, savings from peak utility rates or off-grid power independence, gain peace-of-mind with our reliable energy solutions.
Thank you!