So, this may be a little abnormal for the typical discussions here.
I am an EE trying to design some off-grid systems(or rather augment some off-grid systems) in the 50-150kva range.
We currently operate as generator prime systems with 24/7 generator operation(or very near it). I am trying to make an argument for converting to PV prime with standby generator operation. We have had success with this type of design at smaller facilities, but not at larger facilities.
I know that IEEE 1562 typically recommends a minimum sizing of 5 days for batteries for off-grid applications. I know I can shrink that number if I have a standby EG. I also know that if I shrink that number too much, the "standby EG" will be required to operate on a daily basis.
Example: If I only have 20 hours of battery, my EG will not be a standby generator.
If I have 36 hours of battery, I can be fairly certain I will have a standby generator.
I am trying to figure out, from a design perspective, where IEEE or similar puts that number.
Any thoughts?
I am an EE trying to design some off-grid systems(or rather augment some off-grid systems) in the 50-150kva range.
We currently operate as generator prime systems with 24/7 generator operation(or very near it). I am trying to make an argument for converting to PV prime with standby generator operation. We have had success with this type of design at smaller facilities, but not at larger facilities.
I know that IEEE 1562 typically recommends a minimum sizing of 5 days for batteries for off-grid applications. I know I can shrink that number if I have a standby EG. I also know that if I shrink that number too much, the "standby EG" will be required to operate on a daily basis.
Example: If I only have 20 hours of battery, my EG will not be a standby generator.
If I have 36 hours of battery, I can be fairly certain I will have a standby generator.
I am trying to figure out, from a design perspective, where IEEE or similar puts that number.
Any thoughts?