I had been discussing this but i thought it was hyjacking the original thread.
I had noticed mike posting about the required amps of 5% to 10% to charge a battery with panels and the sums did not work for my system.
I had quite a bit of back and forth with Sunking but was still confused.
I have 2200w of 24 panels to charge them, so 94amps, but this is limited to 80amps by my charge controllers.
Through research today i have found that my battery is 1800ah @ C100 rate.
My battery is 1065ah @ C10 rate,
I read that charging requirements are worked out on the C10 rate.
I had been working the sums on 1800ah, C100 rate this means charge amps are about 4.5%
So for my system it would mean that my 80amps of possible charge is about 7.5% of my C10, 1065ah.
So this works out with Mikes 5% to 10% requirments.
Makes sense to me but am I correct?
I had noticed mike posting about the required amps of 5% to 10% to charge a battery with panels and the sums did not work for my system.
I had quite a bit of back and forth with Sunking but was still confused.
I have 2200w of 24 panels to charge them, so 94amps, but this is limited to 80amps by my charge controllers.
Through research today i have found that my battery is 1800ah @ C100 rate.
My battery is 1065ah @ C10 rate,
I read that charging requirements are worked out on the C10 rate.
I had been working the sums on 1800ah, C100 rate this means charge amps are about 4.5%
So for my system it would mean that my 80amps of possible charge is about 7.5% of my C10, 1065ah.
So this works out with Mikes 5% to 10% requirments.
Makes sense to me but am I correct?
Comment