Hello,
So I just got my Magnum Energy MS4448PAE Inverter/Charger and will be ordering 16 Crown CR430 batteries soon (2 strings of 8, 48V system). I don't think I will ever run this inverter to full capacity but I wanted to have some room to grow beyond my current needs. My question is what will be a good DC wiring setup for this system. I have looked into using copper plate and various types of wire between the batteries but I keep coming back to using 1/0 copper for each battery string, and 4/0 copper for the + & - trunk lines up to the inverter (all wire connections with 5/16" Bare Copper Terminal Lugs).
So I started second guessing my wire selection when I looked up a magnum 100A DC breaker (BR-DC100-BM) which states that it only accepts up to 6AWG wire. huh??? 6AWG is only rated for 37A on the American Wire Gauge chart. What is going on here?
Lastly I knew my 4/0 & 1/0 wire selection was overkill but I want to minimize losses...so in an effort to find the point of diminishing return on increasing the wire size I used the voltage drop calculator found at the link below. I seem to be happy with #2 for the battery strings and 2/0 for the trunk lines based upon the results.
Does this seem reasonable to you? ......and what the heck is up with only #6 on that 100A breaker...makes no sense to me based upon the American Wire Gauge chart.
Thanks
So I just got my Magnum Energy MS4448PAE Inverter/Charger and will be ordering 16 Crown CR430 batteries soon (2 strings of 8, 48V system). I don't think I will ever run this inverter to full capacity but I wanted to have some room to grow beyond my current needs. My question is what will be a good DC wiring setup for this system. I have looked into using copper plate and various types of wire between the batteries but I keep coming back to using 1/0 copper for each battery string, and 4/0 copper for the + & - trunk lines up to the inverter (all wire connections with 5/16" Bare Copper Terminal Lugs).
So I started second guessing my wire selection when I looked up a magnum 100A DC breaker (BR-DC100-BM) which states that it only accepts up to 6AWG wire. huh??? 6AWG is only rated for 37A on the American Wire Gauge chart. What is going on here?
Lastly I knew my 4/0 & 1/0 wire selection was overkill but I want to minimize losses...so in an effort to find the point of diminishing return on increasing the wire size I used the voltage drop calculator found at the link below. I seem to be happy with #2 for the battery strings and 2/0 for the trunk lines based upon the results.
Does this seem reasonable to you? ......and what the heck is up with only #6 on that 100A breaker...makes no sense to me based upon the American Wire Gauge chart.
Thanks