Hey guys, I need some advice here. I've recently changed all the batteries on a system and I want to fuse each string for extra piece of mind. Here are the stats:
System voltage: 24
Bank: 16 us2200 232Ah@6v wired in 4 24V strings. All strings are paralleled together on a bus bar using the exact same length of 2/0 wire.
Power is then fed to a magnum 4024 inverter via a fuse.
Maximum draw from inverter is about 170A but the real maximum draw in real life is 130A. So, correct me if I'm wrong here but normally, the current flowing into each one of the four string shouldn't rise above 42A (170/4). Let's add the 1,25 factor and that brings us to a maximum string current of 52A. Right?
First question: The local shop where I usually buy my stuff gives me a choice between a 50 or 80 amps fuse. I ordered the 50A considering that maximum output of the inverter is never used (I know I shouldn't say never but...). Does that sounds right to you or I should have gone with the 80?
Second question: All the wires paralleling the 4 strings are exact equal length to achieve a proper balance and I want to keep it that way. So, since the fuses will add extra resistance, I figure that, in order to keep that balance, I would need to cut a but of the positive wires (I'm fusing the positive side) to equal the resistance of the negative wires. Right? So, my question is: how am I suppose to figure out what length of wire to cut in order to subtract the resistance of the fuse on each positive line?
Thank you!
System voltage: 24
Bank: 16 us2200 232Ah@6v wired in 4 24V strings. All strings are paralleled together on a bus bar using the exact same length of 2/0 wire.
Power is then fed to a magnum 4024 inverter via a fuse.
Maximum draw from inverter is about 170A but the real maximum draw in real life is 130A. So, correct me if I'm wrong here but normally, the current flowing into each one of the four string shouldn't rise above 42A (170/4). Let's add the 1,25 factor and that brings us to a maximum string current of 52A. Right?
First question: The local shop where I usually buy my stuff gives me a choice between a 50 or 80 amps fuse. I ordered the 50A considering that maximum output of the inverter is never used (I know I shouldn't say never but...). Does that sounds right to you or I should have gone with the 80?
Second question: All the wires paralleling the 4 strings are exact equal length to achieve a proper balance and I want to keep it that way. So, since the fuses will add extra resistance, I figure that, in order to keep that balance, I would need to cut a but of the positive wires (I'm fusing the positive side) to equal the resistance of the negative wires. Right? So, my question is: how am I suppose to figure out what length of wire to cut in order to subtract the resistance of the fuse on each positive line?
Thank you!