I've seen several DIY modifications for UPS (Uninterrupted Power Supply) where instead of using the small normal UPS batteries, the user replaces those batteries with a large (~100 ah) deep cycle battery.  First off, I'm curious how safe this is?  I guess if all the connections are made properly, and the UPS inverter can supply its rated power for the extended time it would be ok.  In any case, I have a couple of UPS units that have dead batteries, and was thinking of attempting this (with extended monitored testing certainly).  My plan was to put a couple of these (UPG UB12350 Amazon Link) in series (my UPS is 24 volt).
The PC I have connected only uses 114 watts max. The UPS has a display screen that tells me output volts and watts, so assuming 95% efficient inventor (is that valid?) my max current draw from the batteries would be 5 amps.
Anything off here? How safe is this?
					The PC I have connected only uses 114 watts max. The UPS has a display screen that tells me output volts and watts, so assuming 95% efficient inventor (is that valid?) my max current draw from the batteries would be 5 amps.
Anything off here? How safe is this?
							
						