I did a off grid calculator by http://www.altenergydesign.com/offgrid.html and it comes up with 48V 906 battery bank amp-hours with a 3 string set up of 302 per string. When I look at batteries I see flooded lead acid batteries around 200Ah. Does that mean I need just a few batteries for the whole system?
I'm confused, how many batteries do I Need?
Collapse
X
-
-
That seems like a lot of batteries. My guess is you're in forklift battery territory.
With your 48 volt, 906 AH, I assume that's daily usage, so you want between two times that 1812 AH to avoid going to 50% depletion, and 2718 AH to go one cloudy day.
906 AH at 48 volts is about 32 golf cart sized 6v FLA batteries. I only mention 6 volt batteries is because my system I have four of those to power my RV a couple of days without a recharge. 6v are light enough at 65 LBS for me to take in and out of my RV as needed.Last edited by chrisski; 11-16-2020, 03:18 PM. -
For a full up house without air cond or forced air heat, I have a 48V 800ah bank. Power is expensive
Batteries in series add Volts. and the amps stay the same ( 12V 200ah battery, 4 in series is 48v 200ah)
batteries in parallel add amp hours, 12v 200ah, 4 in parallel = 12v 800ahPowerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
The other question is if I can add a small wind turbine to augment the panels during night hours and windy cloudy days. The turbine would be the same voltage as the panels. Our location is always windy so I thought this would help with reducing battery bank size by not having to factor in extra cloudy days for my panels. Any thoughts?Comment
-
I have a 48vdc 600ah battery bank. It has been very difficult for me to perform equalizing charges on my batteries. That is something that needs to be considered when designing a system.
4400w, Midnite Classic 150 charge-controller.Comment
-
Unless it's windy enough that you have to tie your hat on, it's not suitable for wind. Most people can't live where it's windy enough for good wind power. Sure, many places have usable wind one day out of the week, but the expense and maintenance of a wind turbine, is not often worth it. A few more PV panels will usually be the easiest and best answer. Having a backup generator is also important too.
Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
The other question is if I can add a small wind turbine to augment the panels during night hours and windy cloudy days. The turbine would be the same voltage as the panels. Our location is always windy so I thought this would help with reducing battery bank size by not having to factor in extra cloudy days for my panels. Any thoughts?
I have seen some turbines on a lake front property or on a boat but even they may not perform as well as the solar panels.Comment
Comment