6 months ago we put in a set of the new Trojan SAGM 06 375 AGM's. X2 banks of 8 units paralleled to copper bus bars w/ equal take off cable lengths etc.
In the first 3 month, batteries reached full charge (i.e. C/200 tail current) in around 4-4.5 hours of absorb.
Daily DOD is around 15- 20% per night.
The last few months, the battery bank is taking much much longer to reach the full charge tail current of C/200, and even after 6.5 hours in absorb, I can only reach about a C/100 tail current. There is no longer anyway I can get to the C/200 tail current in the 8 or so hours of recharge time in the day.
The system is paneled to have the batteries bulk charged by 10:30-11am or so, and we have sun till 5 pm. So despite being paneled correctly for the DOD and having 5+ hours of absorb time daily, I cannot fully charge the bank any longer.
Discharge voltages are also lower and voltage in the morning just before the sun come up, was about 50.2v, but is now about 49,4, so much lower after same DOD, indicating they are not being fully charged.
I am quite experience with batteries and been off grid for 7 years. Bulk and absorb voltages are per Trojan spec sheet and temp compensated etc. I check the bank voltages and each battery voltage during charging as well as under discharge and at high amp loads to see if there is a failing unit/s. I cannot find a problem battery, they are all equal voltage pretty much under load both big and small.
any ideas?
6 months ago we put in a set of the new Trojan SAGM 06 375 AGM's. X2 banks of 8 units paralleled to copper bus bars w/ equal take off cable lengths etc.
In the first 3 month, batteries reached full charge (i.e. C/200 tail current) in around 4-4.5 hours of absorb.
Daily DOD is around 15- 20% per night.
The last few months, the battery bank is taking much much longer to reach the full charge tail current of C/200, and even after 6.5 hours in absorb, I can only reach about a C/100 tail current. There is no longer anyway I can get to the C/200 tail current in the 8 or so hours of recharge time in the day.
The system is paneled to have the batteries bulk charged by 10:30-11am or so, and we have sun till 5 pm. So despite being paneled correctly for the DOD and having 5+ hours of absorb time daily, I cannot fully charge the bank any longer.
Discharge voltages are also lower and voltage in the morning just before the sun come up, was about 50.2v, but is now about 49,4, so much lower after same DOD, indicating they are not being fully charged.
I am quite experience with batteries and been off grid for 7 years. Bulk and absorb voltages are per Trojan spec sheet and temp compensated etc. I check the bank voltages and each battery voltage during charging as well as under discharge and at high amp loads to see if there is a failing unit/s. I cannot find a problem battery, they are all equal voltage pretty much under load both big and small.
any ideas?