I was trying to explain the WHY to a buddy, I understand BIR & cable IR, cable length, etc. and understand that, but can't answer his question of why that is not also issues on batteries in series. What is it specifically about being in series that then resolves the problems the issues with parallel, cables, connections, etc. thanks
Try our solar cost and savings calculator
I know you all say NO to parallel batteries, but
Collapse
X
-
-
Series and parallel circuit laws.
In series current is equal where I1 = I2 = I3 = I4
In parallel the current splits and are not equal.MSEE, PE -
That is pure Rubbish. Current takes all paths available.Originally posted by littleharborcurrent will take the path of least resistance .
By that idiotic logic if you were to put a 1 ohm resistor in parallel with a 10 ohm resistor only the 1 ohm resistor would have current flowing which is pure rubbish. Assuming 1 volt is applied, you would have 1 amp flowing through the 1 ohm resistor, and .1 amp in the 10 ohm resistor for a total current of 1.1 amps.Last edited by Sunking; 04-01-2018, 07:59 PM.MSEE, PEComment
-
Comment
-
ok, clear as mud......so you made me go look up what "I" is which is current. so the current through each of the batteries in series by must be equal, but in parallel they could be different.
But physically why is that so? is there a flow of water analogy, like in parallel each battery is a reservoir that can have slightly different sized inlets and outlets that impacts how easily water can flow in or out of each reservoir on its way the end user, but in series what flows into the first battery must flow through each subsequent battery and out the end, thus no one battery can be less filled than the rest. I'm quessing this isn't right, but can you give a similiar sort of analogy?
And while cabling/connections can impact how freely current flows, thus different IR of cabling/connections can impinge the flow in either parallel or series, the negative consequences of such impingment in parallel connections is the different speeds of filling and emptying of each battery, and thus they can have different levels of "fill" or charge, whereas in series all the batteries must be at an equal level???
Comment
-
Yea, it bugs me too every time someone mentions the shortest path. First mentioned it Sat. Bruce Roe
That is pure Rubbish. Current takes all paths available.
By that idiotic logic if you were to put a 1 ohm resistor in parallel with a 10 ohm resistor only the 1 ohm resistor would have current flowing which is pure rubbish. Assuming 1 volt is applied, you would have 1 amp flowing through the 1 ohm resistor, and .1 amp in the 10 ohm resistor for a total current of 1.1 amps.Comment
-
Each parallel path has a slightly different resistance. That will cause the current amount to also be slightly different. The path with the lowest resistance will receive the highest current.ok, clear as mud......so you made me go look up what "I" is which is current. so the current through each of the batteries in series by must be equal, but in parallel they could be different.
But physically why is that so? is there a flow of water analogy, like in parallel each battery is a reservoir that can have slightly different sized inlets and outlets that impacts how easily water can flow in or out of each reservoir on its way the end user, but in series what flows into the first battery must flow through each subsequent battery and out the end, thus no one battery can be less filled than the rest. I'm quessing this isn't right, but can you give a similiar sort of analogy?
And while cabling/connections can impact how freely current flows, thus different IR of cabling/connections can impinge the flow in either parallel or series, the negative consequences of such impingment in parallel connections is the different speeds of filling and emptying of each battery, and thus they can have different levels of "fill" or charge, whereas in series all the batteries must be at an equal level???
That is based on Ohm's law where E = I x R or (E= voltage, I = current, R = resistance). If E is the same in each "path" then lowering or raising the R value will change the I value in the opposite direction.Comment
-
Comment
-
Comment
-
NP and my following comments are directed to the OP.
In theory if I take two 0.1 Ohm resistors, place then in parallel, apply 1 volt, each resistor will have 10 amps flowing. Ask any teacher or instructor and that is what they will tell you because that is all they know and never done it. In practice it does not work that way.
Now the question should be: WHY NOT?
Real simple, in real practice the resistors will not be equal. Now compound that with the fact cable resistance and contact resistance will not be equal. So now the teacher has to ask a tech, engineer, or sparky how to make it work? KISS (Keep It Simple Stupid) teacher, put the batteries in series.Last edited by Sunking; 04-02-2018, 12:24 PM.MSEE, PEComment
-
Because what really sets the current flow is the equivalent resistances of each path. You will get more current down a lower resistance path due to Ohm's Law. And weaker batteries tend to have higher equivalent resistances. So the better batteries get most of the charge current.
You can only take the water analogy so far.is there a flow of water analogy, like in parallel each battery is a reservoir that can have slightly different sized inlets and outlets that impacts how easily water can flow in or out of each reservoir on its way the end user, but in series what flows into the first battery must flow through each subsequent battery and out the end, thus no one battery can be less filled than the rest. I'm quessing this isn't right, but can you give a similiar sort of analogy?
Lead acid batteries are different than many other batteries in that they have a built in balancing mechanism. If you overcharge them a little they gas out a bit but stay at close to 100% charge. So a series string will eventually balance itself out if you keep charging it (albeit with some loss of electrolyte.) And lead acid batteries want to be kept at a full state of charge.And while cabling/connections can impact how freely current flows, thus different IR of cabling/connections can impinge the flow in either parallel or series, the negative consequences of such impingment in parallel connections is the different speeds of filling and emptying of each battery, and thus they can have different levels of "fill" or charge, whereas in series all the batteries must be at an equal level?
If they are in parallel you can't force that to happen as easily, because most of the charge current will be going to the "better" cell strings that don't need to be balanced in the first place. The weaker strings will be neglected and will not get full balancing charges.
Note that this is unique to lead acid, which is why chemistries like LiFePO4 have very different requirements for balancing, monitoring and charging.Comment
-
Comment
-
Not could be, they will be different. Read my reply in post 10
You are making the same mistake an academic makes. You assume everything is equal and fair. That is not real. You have assumed every cell in a series string is at the same SOC and capacities are equal. They are not equal. Most batteries, there are some exceptions like lithium, are self equalizing with respect to SOC. Lead Acid batteries are self equalizing. When a cell reaches 100% SOC will still pass charge current and hold 100% SOC. What it does is goes into gassing voltage and you start electrolysis of the water. Result is you start using water and heating the cell up as waste products because the battery is now consuming power rather than storing power. It is a good thing assuming the other cells are healthy.But physically why is that so? is there a flow of water analogy, like in parallel each battery is a reservoir that can have slightly different sized inlets and outlets that impacts how easily water can flow in or out of each reservoir on its way the end user, but in series what flows into the first battery must flow through each subsequent battery and out the end, thus no one battery can be less filled than the rest. I'm quessing this isn't right, but can you give a similiar sort of analogy?
Again you are not grasping Series and Parallel circuit Laws. Think of series circuit as a 1-lane highway. Everyone must go the same speed and follow the same path. Think of parallel as a multi-lane highway where weak ole grandpa and slower drivers keep right. Or better yet study Series/Parallel circuits.And while cabling/connections can impact how freely current flows, thus different IR of cabling/connections can impinge the flow in either parallel or series, the negative consequences of such impingment in parallel connections is the different speeds of filling and emptying of each battery, and thus they can have different levels of "fill" or charge, whereas in series all the batteries must be at an equal level???
Just do not make the mistake academics and teacher make assuming the resistances are equal. That only happens on paper, not the real world.In a series circuit, the current through each of the components is the same, and the voltage across the circuit is the sum of the voltages across each component. In a parallel circuit, the voltage across each of the components is the same, and the total current is the sum of the currents through each component.Last edited by Sunking; 04-03-2018, 11:26 AM.MSEE, PEComment
Copyright © 2014 SolarReviews All rights reserved.
Powered by vBulletin® Version 6.1.3
Copyright © 2026 MH Sub I, LLC dba vBulletin. All rights reserved.
Copyright © 2026 MH Sub I, LLC dba vBulletin. All rights reserved.
All times are GMT-5. This page was generated at 01:15 AM.
Comment