The point is: Even with the best of engineering, one cannot factor out manufacturing variations. In a parallel array of batteries there is going be some imbalance because of manufacturing variations in the cells that compose a battery. For this reason, if one can do a one series string battery bank, one would be better off doing a one series string battery bank instead of a parallel battery bank. A one series string battery bank produces the longest life span and the lowest required maintenance ... better ROI and lower overhead.
About to buy an AGM battery bank. Anything new or economical I should consider?
Collapse
X
-
-
For my last series bank, I used 2/0 cable, with copper terminals that I crimped at West Marine, soldered afterwards, and then used heat shrink tubing on to cover as much as possible. Is that enough?
Oh, I've been wondering this, can the cables connecting the batteries in series be different lengths?Comment
-
It depends. If the cable lengths are symmetrical from the midpoint to both end points, It will be OK. If the cable lengths are asymmetrical from the midpoint to both end points, there will be a voltage imbalance across the batteries. Keep it as symmetrical as possible and the shortest possible lengths best results.Last edited by Falsa_Nominis; 04-03-2018, 01:07 AM.Comment
-
It depends. If the cable lengths are symmetrical from the midpoint to both end points, It will be OK. If the cable lengths are asymmetrical from the midpoint to both end points, there will be a voltage imbalance across the batteries. Keep it as symmetrical as possible and the shortest possible lengths best results.
Comment
-
It depends. If the cable lengths are symmetrical from the midpoint to both end points, It will be OK. If the cable lengths are asymmetrical from the midpoint to both end points, there will be a voltage imbalance across the batteries. Keep it as symmetrical as possible and the shortest possible lengths best results.
Comment
-
Comment
-
Comment
-
Many people will undersize the battery bank because they do not develop an energy usage profile before building the system. By the time they realize the mistake, they will be economically locked into a battery bank voltage. Their only economical option will be to expand the battery bank by going to a series-parallel battery bank.
Over the years I have tried to get people to develop energy usage profiles before building but the success rate is not very good. Many either cannot do the math or they choose to follow somebody else that does not understand the value of an energy usage profile.
By teaching people to be uniform with series interconnect cables, I am teaching them a practice that can benefit them later.
If others choose to teach sloppy wiring practices and deal with the fall out later, that is their decision and they can deal with the fallout.
Last edited by Falsa_Nominis; 04-03-2018, 04:36 PM.Comment
-
It depends. If the cable lengths are symmetrical from the midpoint to both end points, It will be OK. If the cable lengths are asymmetrical from the midpoint to both end points, there will be a voltage imbalance across the batteries. Keep it as symmetrical as possible and the shortest possible lengths best results.
Continue giving erroneous information, and you get longer vacations.Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
a) wicks solder up the cable in an uncontrolled manner
b) the heat of soldering damages the insulation
c) a properly crimped connector is gas tight, and has no room between the strands to wick solder into the joint
d) if a connector relies on solder, under high amps, the solder can melt and let the wire fall out
Oh, I've been wondering this, can the cables connecting the batteries in series be different lengths?
Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
Comment
-
Stick with properly compressed compression terminals using approved tooling and terminals. A properly terminated terminal is stronger the the wire it is connected to and the extreme pressures homogenize the conductors effectively weld them electrically for the lowest resistance possible. So I have no issue over sizing cables. But with any of them larger than 6 AWG, have a Marine, Cable Shop, electrician, or buy terminated cables. Consumers just do not have the tooling and experience.
OK off my soap box.
What I do suggest for all RV users out there is use Marine Rated Cable and Devices. To size your wiring needs use the following table 3% column. Example if you have a 50 amp fuse and 1-way distance will require 4 AWG.
Last edited by Sunking; 04-03-2018, 08:18 PM.MSEE, PEComment
-
So to sum up - your claim that "If the cable lengths are asymmetrical from the midpoint to both end points, there will be a voltage imbalance across the batteries" in series strings is incorrect.
Good, now that that's out of the way -
If others choose to teach sloppy wiring practices and deal with the fall out later, that is their decision and they can deal with the fallout.Last edited by jflorey2; 04-04-2018, 01:27 PM.Comment
-
You got it backwards. Non equal lengths compounds the problem for PARALLEL batteries you idiot. You are on my radar and a target. You are also on the moderators radar and other engineers ready to attack you. Understand? Now go away.
Last edited by Sunking; 04-03-2018, 08:53 PM.MSEE, PEComment
-
Copy that. Never solder terminals again. What about the inter-cell cables, what gauge should I use? I can probably order premade ones, right?Comment