Is there anyway to SAFELY heat a battery box?

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • spike001
    Junior Member
    • Jan 2013
    • 14

    #16
    Originally posted by inetdog
    Since you will have a data transmission link, I assume that you have already planned for the battery voltage and temperature to be recorded and transmitted too? To give you a good handle on the state of the system, an indication of the panel current would be very nice to have. The panel voltage will not change much as a function of light level, but the current will. The voltage will change as a function of temperature and the Vmp chosen by the CC will vary considerably if there is partial shading of a series string.
    If possible the data transmission should be done toward the end of the hours the panels are producing so that the extra power drain can be provided directly by the panels rather than cycling the batteries. (Assuming that data transmission will take significant power.)

    Sorry if I am hitting things you have already planned for, I am just free-associating here.
    No problem on the free associating.....I'd rather have that than an "oops" moment. But you also bring up a good point. I have two sets of CCs at this point and need to investigate all of the functions. One has an RJ45 jack which I assume....I mean hope that I can plug directly into my hub so that I can pull data from it directly. I plan on doing most of my "communicating" with the set up mid-day so that I can take advantage of the fact that the panels are producing some power. Since the sun sets at around 4pm I'll most likely let the system idle/sleep unless I have a necessity to wake it up. Surprisingly the power required to run the cellular hub and transmits is approximately 18W....so it isn't terrible. But I'll be able to validate all of these factors once I get the system connected end-to-end. Thanks for the free association.

    Comment

    • inetdog
      Super Moderator
      • May 2012
      • 9909

      #17
      Originally posted by spike001
      But you also bring up a good point. I have two sets of CCs at this point and need to investigate all of the functions. One has an RJ45 jack which I assume....I mean hope that I can plug directly into my hub so that I can pull data from it directly.
      Chances are very good that the RJ-45 jack is a serial bus interface with differential send and receive drivers (such as Modbus) rather than Ethernet. But some CCs and inverters do have the option for an Ethernet interface card to be installed instead. Or you can just get a USB to Modbus adapter and talk directly using the appropriate software. Some of the members have discussed Open Source software that they are working on for this purpose.
      SunnyBoy 3000 US, 18 BP Solar 175B panels.

      Comment

      • Mike90250
        Moderator
        • May 2009
        • 16020

        #18
        Some questions for you to ponder.

        While AGM's can handle low temperatures better than flooded, their chemistry still fails and your amp hour capacity degrades as temperature goes low.

        So what is the plan for the 11th cloudy day? Will you have a generator to save the batteries ? Even AGM batteries will begin to sulfate when below 70% of full.

        Massively parallel banks are not good. Consider upping the system voltage to 24, or even 48V to avoid parallel strings.

        Extreme cold will temperature cycle/de-torque the fasteners, and you may need SS spring washers to keep tight terminal connections. I've not had experience with lead terminals in extreme cold. DO make sure your controllers can handle the cold environment.
        And maybe redundant PV arrays would be called for, as the cold will really be stressing the tab connections in the panels. Again, no experience here, but work with spacecraft makes me think of all the things that happen in cold environments.

        As for thermal control, the freeze point of water, requires/releases a lot of BTU's to cycle from 31 - 33F, and there are lots of phase change thermal materials used in the 60-90F range, you may want to research if there is anything usable in your critical range. Remember, once the electrolyte in a battery freezes, the battery is unusable till the whole thing thaws. If you pump power into it, only small areas will thaw, then boil and vent, depleting your electrolyte reserves at best, and destroying the battery at worse.

        I wonder if super caps will work at these low temps ? What about other battery chemistry ? Any primary batteries (zinc air) ?
        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

        solar: http://tinyurl.com/LMR-Solar
        gen: http://tinyurl.com/LMR-Lister

        Comment

        • spike001
          Junior Member
          • Jan 2013
          • 14

          #19
          Originally posted by Mike90250
          Some questions for you to ponder.

          While AGM's can handle low temperatures better than flooded, their chemistry still fails and your amp hour capacity degrades as temperature goes low.

          So what is the plan for the 11th cloudy day? Will you have a generator to save the batteries ? Even AGM batteries will begin to sulfate when below 70% of full.

          Massively parallel banks are not good. Consider upping the system voltage to 24, or even 48V to avoid parallel strings.

          Extreme cold will temperature cycle/de-torque the fasteners, and you may need SS spring washers to keep tight terminal connections. I've not had experience with lead terminals in extreme cold. DO make sure your controllers can handle the cold environment.
          And maybe redundant PV arrays would be called for, as the cold will really be stressing the tab connections in the panels. Again, no experience here, but work with spacecraft makes me think of all the things that happen in cold environments.

          As for thermal control, the freeze point of water, requires/releases a lot of BTU's to cycle from 31 - 33F, and there are lots of phase change thermal materials used in the 60-90F range, you may want to research if there is anything usable in your critical range. Remember, once the electrolyte in a battery freezes, the battery is unusable till the whole thing thaws. If you pump power into it, only small areas will thaw, then boil and vent, depleting your electrolyte reserves at best, and destroying the battery at worse.

          I wonder if super caps will work at these low temps ? What about other battery chemistry ? Any primary batteries (zinc air) ?
          Lots of good items to take into consideration. My immediate problem is the impact days of autonomy and temperature are having on the size, and hence, cost of a quality battery bank. At this point I may just have to roll back the project objectives and go with a less costly set of goals as a proof of concept....in warm weather.

          Comment

          • Sunking
            Solar Fanatic
            • Feb 2010
            • 23301

            #20
            Spike what is the:

            Location
            Daily watt hour consumption
            MSEE, PE

            Comment

            • spike001
              Junior Member
              • Jan 2013
              • 14

              #21
              Originally posted by Sunking
              Spike what is the:

              Location
              Daily watt hour consumption
              Hi Sunking - info below as requested.

              Location: Latitude 46.2 degrees North by Longitude 70.0W

              The daily Watt hour consumption is 566 Watts.

              The worse month of for insolation is Dec @1.15 kWh/m^2 per day

              When I used the formulas provided by concorde and factored in 10 days of automony a their design factor based on temp (which I think was approximately 2.25 or thereabouts) that battery bank got quite large. I also ran the numbers throught the works sheets provided by SEI and received similar results. Thoughts? Am I missing something? Thanks Sunking, spike

              Comment

              • Sunking
                Solar Fanatic
                • Feb 2010
                • 23301

                #22
                Originally posted by spike001
                Hi Sunking - info below as requested.

                Location: Latitude 46.2 degrees North by Longitude 70.0W

                The daily Watt hour consumption is 566 Watts.

                The worse month of for insolation is Dec @1.15 kWh/m^2 per day

                When I used the formulas provided by concorde and factored in 10 days of automony a their design factor based on temp (which I think was approximately 2.25 or thereabouts) that battery bank got quite large. I also ran the numbers throught the works sheets provided by SEI and received similar results. Thoughts? Am I missing something? Thanks Sunking, spike
                No you got it right. You are screwed. You are looking at a 1000 watt panel wattage, 80 amp controller, and 400 AH 12 volt AGM battery.

                Good news is summer will be no problem.
                MSEE, PE

                Comment

                • spike001
                  Junior Member
                  • Jan 2013
                  • 14

                  #23
                  Originally posted by Sunking
                  No you got it right. You are screwed. You are looking at a 1000 watt panel wattage, 80 amp controller, and 400 AH 12 volt AGM battery.

                  Good news is summer will be no problem.
                  Love your honesty....lol....but frankly I would have been just as happy to be wrong. I am seriously considering putting together a much smaller summer version.....at least I can verify the proof of concept. Interestingly the Canadian government tendered an RFQ about a month or so go for the far Arctic for something very close to this (major difference being satellite (not cellular) and that they are willing to pay to send someone up there on schedule to maintain it.....I took a quick look at it and figured that it will run them about $1M (ballpark)once they get the thing designed, depolyed, managed and maintained. Plus it is government....so our money.

                  If you don't mind - I just have one last question for you. Do you use a tool to make your design calcls? or do you depend on something likes the worksheets that SEI provides?

                  Otherwise great working with you - I was really looking forward to working with the Concorde AGM product - perhaps my next project! spike

                  Comment

                  • Naptown
                    Solar Fanatic
                    • Feb 2011
                    • 6880

                    #24
                    Originally posted by spike001
                    Love your honesty....lol....but frankly I would have been just as happy to be wrong. I am seriously considering putting together a much smaller summer version.....at least I can verify the proof of concept. Interestingly the Canadian government tendered an RFQ about a month or so go for the far Arctic for something very close to this (major difference being satellite (not cellular) and that they are willing to pay to send someone up there on schedule to maintain it.....I took a quick look at it and figured that it will run them about $1M (ballpark)once they get the thing designed, depolyed, managed and maintained. Plus it is government....so our money.

                    If you don't mind - I just have one last question for you. Do you use a tool to make your design calcls? or do you depend on something likes the worksheets that SEI provides?

                    Otherwise great working with you - I was really looking forward to working with the Concorde AGM product - perhaps my next project! spike
                    Here's one I made up that is posted here.
                    It does not take into account extreme cold and heat on the batteries.
                    Discuss remote solar applications for homes, cabins, RV and boats. If you have a question on equipment for an off grid system, such as charge controllers or inverters, then post your question in this forum.
                    NABCEP certified Technical Sales Professional

                    [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

                    [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

                    [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

                    Comment

                    • spike001
                      Junior Member
                      • Jan 2013
                      • 14

                      #25
                      Originally posted by Naptown
                      Here's one I made up that is posted here.
                      It does not take into account extreme cold and heat on the batteries.
                      http://www.solarpaneltalk.com/showth...Battery-Design
                      Thanks it's going into my reference file!

                      Comment

                      • Sunking
                        Solar Fanatic
                        • Feb 2010
                        • 23301

                        #26
                        Originally posted by spike001
                        If you don't mind - I just have one last question for you. Do you use a tool to make your design calcls? or do you depend on something likes the worksheets that SEI provides?
                        I do a lot of work for cellular telephone companies in remote areas without commercial power in the Dessert SW along Interstate highways and Indian Reservations. They are pretty easy burning a continuous 250 watts 24 hours a day consuming 6 Kwh/day. I use a custom made spreadsheet with Macros to link into NREL to gather Insolation numbers, temperatures, various manufactures data, derating etc. Takes about 1 minute to do a design with parts list and basic drawings. Pretty sweet gig when they come up; cost plus 15%. Telcos got big bucks and strict overkill standards. Typical bill is $80K, plus rework every few years replacing batteries. They maintain the equipment, generator, and fuel. I just collect a check and push some buttons, mail out some bids, go to the site at least once, and push some paper.
                        MSEE, PE

                        Comment

                        • inetdog
                          Super Moderator
                          • May 2012
                          • 9909

                          #27
                          Originally posted by Sunking
                          I do a lot of work for cellular telephone companies in remote areas without commercial power in the Dessert SW along Interstate highways and Indian Reservations. They are pretty easy burning a continuous 250 watts 24 hours a day consuming 6 Kwh/day. I use a custom made spreadsheet with Macros to link into NREL to gather Insolation numbers, temperatures, various manufactures data, derating etc. Takes about 1 minute to do a design with parts list and basic drawings. Pretty sweet gig when they come up; cost plus 15%. Telcos got big bucks and strict overkill standards. Typical bill is $80K, plus rework every few years replacing batteries. They maintain the equipment, generator, and fuel. I just collect a check and push some buttons, mail out some bids, go to the site at least once, and push some paper.
                          As the classic story goes:
                          "Itemized bill
                          Marking X on side of generator $1
                          Knowing where to mark X on side of generator $9,999."
                          SunnyBoy 3000 US, 18 BP Solar 175B panels.

                          Comment

                          • spike001
                            Junior Member
                            • Jan 2013
                            • 14

                            #28
                            Originally posted by Sunking
                            I do a lot of work for cellular telephone companies in remote areas without commercial power in the Dessert SW along Interstate highways and Indian Reservations. They are pretty easy burning a continuous 250 watts 24 hours a day consuming 6 Kwh/day. I use a custom made spreadsheet with Macros to link into NREL to gather Insolation numbers, temperatures, various manufactures data, derating etc. Takes about 1 minute to do a design with parts list and basic drawings. Pretty sweet gig when they come up; cost plus 15%. Telcos got big bucks and strict overkill standards. Typical bill is $80K, plus rework every few years replacing batteries. They maintain the equipment, generator, and fuel. I just collect a check and push some buttons, mail out some bids, go to the site at least once, and push some paper.
                            Sounds like great work......and I assume no snow. It is STILL snowing here and I'm not even up north. Thanks for your time today. spike

                            Comment

                            • Naptown
                              Solar Fanatic
                              • Feb 2011
                              • 6880

                              #29
                              Originally posted by Sunking
                              I do a lot of work for cellular telephone companies in remote areas without commercial power in the Dessert SW along Interstate highways and Indian Reservations. They are pretty easy burning a continuous 250 watts 24 hours a day consuming 6 Kwh/day. I use a custom made spreadsheet with Macros to link into NREL to gather Insolation numbers, temperatures, various manufactures data, derating etc. Takes about 1 minute to do a design with parts list and basic drawings. Pretty sweet gig when they come up; cost plus 15%. Telcos got big bucks and strict overkill standards. Typical bill is $80K, plus rework every few years replacing batteries. They maintain the equipment, generator, and fuel. I just collect a check and push some buttons, mail out some bids, go to the site at least once, and push some paper.
                              I think I hate you
                              NABCEP certified Technical Sales Professional

                              [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

                              [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

                              [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

                              Comment

                              • SunEagle
                                Super Moderator
                                • Oct 2012
                                • 15147

                                #30
                                Originally posted by Naptown
                                I think I hate you
                                If you didn't feel that way now you will that way when he heads off to a nice warm island living or was it panama? I forget..

                                Comment