Hi,
I have a problem with my solar set up on my travel trailer that I'm hoping someone can help with. I'll provide as much info as I can:
100W solar panel on the roof
GoPower! GP-PWM-30-SQ charge controller (now on my second unit - first one was replaced by the manufacturer for doing exactly what the second one is now doing - described below)
12V wet battery
All of the above is factory install - we purchased the trailer new earlier this year.
When we first got the trailer, solar system seemed to be working as it should.
A few weeks ago, the charge controller started to occasionally give a reading of "low solar" in bright sunlight.
Did some troubleshooting with the manufacturer - checked voltage from the panel - was within spec (about 20V in bright sunlight). Checked amps - ditto - about 3 amps in bright sunlight.
Battery voltage read the same at the battery terminals as the charger was displaying.
They sent me a new charge controller.
Connected the wires (battery first, while solar panel was covered with a heavy moving blanket, then solar panel). Set the battery type to wet.
It registered solar energy (solid red LED) and charging (solid blue LED) BUT was not reading any amps / Ah and was not causing the battery voltage to increase (i.e. was not charging).
Yesterday, I disconnected the solar panel, took voltage and amps readings (both where they should be) and when I reconnected it, it fired up and actually was charging the battery - showed 3.1 amps and the Ah started ticking up as time went by.
I figured I had it licked.
Today I just took a look - it's beaming down bright sunlight and the sun is almost directly overhead, and it's giving me "low solar" again. So I disconnect the panel, take a reading - all good. Reconnect, and it starts working properly again.
So I guess my question is - what would cause this thing to read "low solar" when it's clearly about as good as it gets in terms of solar power AND why is it all good when I disconnect and reconnect?
Keep in mind, this is a replacement unit they sent me (charge controller) due to this behaviour on the first unit. While it's possible, I'd be surprised if I received two defective units in a row.
Also keep in mind, the first one worked great for a few months, then it started doing what I describe above (first unit) and now same thing is happening on the replacement unit. This would suggest that the issue is not the charge controller.
But if it's the solar panel, why does it give good readings, and then everything works great when it's reconnected?
Hoping someone can sort through this and give me some ideas.
I have ordered a new charge controller made by a different manufacturer to see if I get similar results, and then at least I can rule something out as the issue.
Thanks for any help you're able to provide.
Andy
I have a problem with my solar set up on my travel trailer that I'm hoping someone can help with. I'll provide as much info as I can:
100W solar panel on the roof
GoPower! GP-PWM-30-SQ charge controller (now on my second unit - first one was replaced by the manufacturer for doing exactly what the second one is now doing - described below)
12V wet battery
All of the above is factory install - we purchased the trailer new earlier this year.
When we first got the trailer, solar system seemed to be working as it should.
A few weeks ago, the charge controller started to occasionally give a reading of "low solar" in bright sunlight.
Did some troubleshooting with the manufacturer - checked voltage from the panel - was within spec (about 20V in bright sunlight). Checked amps - ditto - about 3 amps in bright sunlight.
Battery voltage read the same at the battery terminals as the charger was displaying.
They sent me a new charge controller.
Connected the wires (battery first, while solar panel was covered with a heavy moving blanket, then solar panel). Set the battery type to wet.
It registered solar energy (solid red LED) and charging (solid blue LED) BUT was not reading any amps / Ah and was not causing the battery voltage to increase (i.e. was not charging).
Yesterday, I disconnected the solar panel, took voltage and amps readings (both where they should be) and when I reconnected it, it fired up and actually was charging the battery - showed 3.1 amps and the Ah started ticking up as time went by.
I figured I had it licked.
Today I just took a look - it's beaming down bright sunlight and the sun is almost directly overhead, and it's giving me "low solar" again. So I disconnect the panel, take a reading - all good. Reconnect, and it starts working properly again.
So I guess my question is - what would cause this thing to read "low solar" when it's clearly about as good as it gets in terms of solar power AND why is it all good when I disconnect and reconnect?
Keep in mind, this is a replacement unit they sent me (charge controller) due to this behaviour on the first unit. While it's possible, I'd be surprised if I received two defective units in a row.
Also keep in mind, the first one worked great for a few months, then it started doing what I describe above (first unit) and now same thing is happening on the replacement unit. This would suggest that the issue is not the charge controller.
But if it's the solar panel, why does it give good readings, and then everything works great when it's reconnected?
Hoping someone can sort through this and give me some ideas.
I have ordered a new charge controller made by a different manufacturer to see if I get similar results, and then at least I can rule something out as the issue.
Thanks for any help you're able to provide.
Andy