Blew a 250 amp fuse the other day. How to avoid this

Collapse
X
 
  • Time
  • Show
Clear All
new posts

  • neweclipse
    replied
    Originally posted by Ampster

    The problem was that the inverter was overloaded by the Air Conditioner when shore power was disconnected. Why do you think a sub panel was not a solution? My understanding was that the proposed sub panel would be powered by shore power and AC would only run from subpanel.
    Originally posted by jflorey2
    Sub panel is simple and bulletproof. Simple and safe are two big factors here.
    Yes, I stand corrected, a sub-panel is a Perfect Solution.

    Leave a comment:


  • Skwidward
    replied
    Originally posted by neweclipse
    So you are content with your manual/human dependent interaction over an automatic no-brainer solution, hope you sleep well.
    Can't imagine it fun to wake up dead...nothing new, but mis-calculations sometimes can cause bad things...

    BTW: The sub-panel alone was never a solution to your problem...relay or relay plus sub-panel was.
    Everybody pay attention

    I'm going to explain why the sub-panel nor the relay are necessary:

    My inverter has a switch on it. "On," Off," or "Charger only."

    The "Charger only" setting solves my problem. I mentioned this twice, already, but maybe I need to explain why.

    My problem: When I am plugged into shore power and I am running my air conditioner, if I lose shore power, my inverter will take over and pull 12V DC power from the batteries and invert it into 120V AC and try to run the air conditioner. I do not want this, as the air conditioner draws WAY too much power when the compressor kicks in. The inverter will try anyway. My fuses will blow to protect the wires (see OP).

    The solution: When I plug into shore power, I flip the switch on my inverter's remote to "charge only." This allows 120V AC to flow from shore power through my inverter and power my TT's 120V AC appliances, such as the air conditioner. If shore power is lost, every single 120V AC appliance in my TT will shut off. The inverter will NOT tap the batteries and try to invert their 12V DC power into 120V AC to power the 120V AC appliances in the TT, as it is turned off. It is in "charge only" mode.. not "on" (inverter) mode. This is sooooooo much simpler than a sub-panel or a relay, and I'm confused why no one suggested it as an option. I find it hard to believe no one else on this forum has an inverter/charger.

    In more simple terms: if I set my inverter to "charge only" mode, it's like I don't have an inverter, and the only power I get is from shore power. If the shore power shuts off, no more power.

    And yeah, the sub-panel would absolutely have been a solution to my problem. I'm glad I don't have to F with it, though.

    Leave a comment:


  • jflorey2
    replied
    Originally posted by neweclipse
    BTW: The sub-panel alone was never a solution to your problem...relay or relay plus sub-panel was.
    Sub panel is simple and bulletproof. Simple and safe are two big factors here.

    Leave a comment:


  • Ampster
    replied
    Originally posted by neweclipse
    ..........BTW: The sub-panel alone was never a solution to your problem...relay or relay plus sub-panel was.
    The problem was that the inverter was overloaded by the Air Conditioner when shore power was disconnected. Why do you think a sub panel was not a solution? My understanding was that the proposed sub panel would be powered by shore power and AC would only run from subpanel.

    Leave a comment:


  • neweclipse
    replied
    So you are content with your manual/human dependent interaction over an automatic no-brainer solution, hope you sleep well.
    Can't imagine it fun to wake up dead...nothing new, but mis-calculations sometimes can cause bad things...

    BTW: The sub-panel alone was never a solution to your problem...relay or relay plus sub-panel was.
    Last edited by neweclipse; 06-14-2019, 09:42 AM.

    Leave a comment:


  • Skwidward
    replied
    Originally posted by Driggs-Dave
    I'll try another approach.....you have two fuses in series, one at the battery and one under the bed, they will have the same current flow.
    Do they look the same?
    Or is one holder blackened and the other like new?

    If you only smoked one of them I'd replace that fuse holder, it could have been defective.

    Just another thought, most travel trailers will charge the house battery from the tow vehicle, did you remove the battery connection to the 7 way plug?
    Both fuse holders are the same and look the same. The cover on the one that blew has an area on it that looks like a lighter had been held under it. I posted a video of an ANL fuse blowing. Neither fuse holder is “blackened.”

    I am replacing the fuse that blew with a circuit breaker, as I mentioned before.

    The fuse holder is actually a piece of acrylic with two 5/16” studs. The ANL fuse sits on the studs and is held in place with nuts. It was not and is not defective-it’s two nuts and two bolts. The fuse was not defective. The fact that the fuse blew when the inverter tried to run the air conditioner off the batteries indicates that it was not defective.

    My battery bank is not connected to the trailer connector. Apparently it never was. I found that strange.

    Either way, the concern I had in the OP is solved as easy as me flicking a switch on the inverter’s remote panel. No need to add a sub panel. No need to try and figure out how to rig up a relay. Just flick a switch and done.

    Leave a comment:


  • Driggs-Dave
    replied
    I'll try another approach.....you have two fuses in series, one at the battery and one under the bed, they will have the same current flow.
    Do they look the same?
    Or is one holder blackened and the other like new?

    If you only smoked one of them I'd replace that fuse holder, it could have been defective.

    Just another thought, most travel trailers will charge the house battery from the tow vehicle, did you remove the battery connection to the 7 way plug?

    Leave a comment:


  • Skwidward
    replied
    Originally posted by Mike90250
    I'm very uncomfortable trying to instruct someone how to construct a transfer switch with a couple relays.

    If you DO NOT know how to work with Grid power, 240 V AC circuits, instructions over the internet are not the best way to learn.
    100% agree

    Leave a comment:


  • Mike90250
    replied
    I'm very uncomfortable trying to instruct someone how to construct a transfer switch with a couple relays.

    If you DO NOT know how to work with Grid power, 240 V AC circuits, instructions over the internet are not the best way to learn.

    Leave a comment:


  • Skwidward
    replied
    So here’s an easier fix to avoid blowing any fuses if you have a system like mine:

    Turn the inverter to “charge only” when plugged in.

    It’s that simple.

    Leave a comment:


  • jflorey2
    replied
    Originally posted by Skwidward
    I am completely ignorant of the relay. I'd be super grateful if you wouldn't mind explaining how to go about setting it up.
    From before:

    If you want to run the A/C only when shore power is present, you might consider a 120VAC relay connected to shore power that enables the air conditioner. Easiest way to do that is via the thermostat line (if you have a separate thermostat.) You can also switch the power to the A/C itself.

    More detail:

    Take a 120VAC DPDT relay. Wire the coil to the incoming (shore) power. You can connect it right there at the input, so close that there's effectively no chance it will short to anything. If you use anything other than a short wire, use a 1 amp fuse between hot and relay to protect the hot wire.

    Now the relay will click ON when there is shore power available, and OFF when there is no shore power available. To be more specific, the common contacts of the relay will connect to the NC (normally closed) contacts when there is no shore power, and connect to the NO (normally open) contacts when there is shore power.

    You now have two choices.

    The easiest is if you have a separate thermostat. If you do, cut one wire of the thermostat lead and connect the two ends to the relay - one to a common pin and the other to the associated NO pin. Now the thermostat will be disconnected when shore power is not available and the A/C will not start, thinking the trailer is already cool.

    The second way is to run the power for the A/C through the relay. Take hot and neutral from your panel's A/C circuit breaker and put them on the common pins of the relay. Connect the A/C itself to the NO pins of the relay. Now the relay will physically disconnect power to the A/C when there is no shore power. If you go this route ensure that the relay contacts are rated for whatever current the A/C pulls.

    Leave a comment:


  • Skwidward
    replied
    Originally posted by neweclipse
    You missed the relay entirely.
    My apologies. The sub panel idea made a lot of sense to me, and I was grateful for the suggestion; as I would not have been able to come up with such a plan on my own. However, I am unsure about the jumper or no jumper part I mentioned above. Evidently this "relay" is something entirely different.

    Originally posted by neweclipse
    The relay alone could drop the A/C by itself (no sub-panel required) or for more loads/circuits, drop the whole "Shore Power ONLY sub-panel" and any circuits that are provided by it.
    Two different approaches as for electrical hardware needed goes.
    I am completely ignorant of the relay. I'd be super grateful if you wouldn't mind explaining how to go about setting it up.

    Leave a comment:


  • neweclipse
    replied
    You missed the relay entirely.

    The relay alone could drop the A/C by itself (no sub-panel required) or for more loads/circuits, drop the whole "Shore Power ONLY sub-panel" and any circuits that are provided by it.
    Two different approaches as for electrical hardware needed goes.

    Leave a comment:


  • Skwidward
    replied
    Originally posted by neweclipse
    Do you understand the application of the mentioned relay to instantly disable the running of the A/C upon loss of shore power?
    I think so. There’s one part I’m not sure about, though.

    Sub panel with two circuit breakers. Shore power in. Shore power out and Air conditioner out. This way the air conditioner is dependent on “true” shore power; shore power is lost, air conditioner receives no power.

    What I’m not too sure about is:

    one hot (black) wire from shore power is wired into the main breaker (of this new subpanel), one neutral (white) wire from shore power is wired into the neutral bus bar, and one ground (green) wire from shore power is wired to the ground bus bar. Coming out the other side of this subpanel would be one hot (black) wire from the “bottom” of the circuit breaker, from the neutral bus bar one neutral (white) wire, from the ground bus bar one ground (bare copper, as I used UF). These 3 wires would combine to form my 10/2 UF that would run to my inverter’s ac in— I’ve got this part.

    So inside this new subpanel sitting next to the main circuit breaker with the shore power will be the circuit breaker for the air conditioner. Out of the “bottom” of this breaker will be one hot (black), from the neutral bus bar there will be a second neutral (white) wire (the shore power being the first), from the ground bus bar will be a second bare copper ground (the shore power being the first). These 3 wires will combine to form the 12/2 romex that runs to the air conditioner.

    Will I need to put a jumper in the “top” of the air conditioner’s circuit breaker from the “top” of the shore power “main” circuit breaker, or will the air conditioner’s circuit breaker receive “hot” power from the bar it clicks onto inside the subpanel next to the shore power circuit breaker?

    Leave a comment:


  • neweclipse
    replied
    Do you understand the application of the mentioned relay to instantly disable the running of the A/C upon loss of shore power?
    Last edited by neweclipse; 06-12-2019, 07:56 AM. Reason: added word "instantly"