Inverter Ground Connections
The inverter's manual says there is a risk of electrical shock if the inverter is not grounded. Still, I see you are correct about GFCI. I clearly didn't understand how they operated before this prompted me to look it up. Thank you.Comment
I think you and I were talking about the first one concerning the chassis. And Sunking was talking about the second which is not required for the GFIC protected inverters to work.Comment
There are technically 2 grounding systems. One is for the metal equipment enclosure and panel frames. The other is associated with the neutral wire in an AC system or Neg wire in a DC system.
A typical transfer switch will only switch the ungrounded conductors (one wire for straight 120, two wires for 120/240). But if there is a bond between neutral and ground on the grid/shore supply side to comply with NEC, then the transfer switch must have an extra pole to disconnect the house neutral from the grid neutral so that an MSW inverter that requires an isolated neutral can be used.SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment
And while we are clarifying, a transfer switch of some kind (or mechanically interlocked breakers or a single male inlet that gets one female cord or the other) is required whenever there will be the possibility of a grid connection and an inverter connection to feed the same wiring at different times.
A typical transfer switch will only switch the ungrounded conductors (one wire for straight 120, two wires for 120/240). But if there is a bond between neutral and ground on the grid/shore supply side to comply with NEC, then the transfer switch must have an extra pole to disconnect the house neutral from the grid neutral so that an MSW inverter that requires an isolated neutral can be used.Comment
Electricians have a neat little trick when they work on stick built homes wired with Romex and plastic boxes. They work on the wiring bare handed on live circuits. How do they do it? They know what they are doing, and disconnect the house ground while they work so they will not be shocked.
Some which are immune to the pain will test for a live circuit with their fingers. They touch their pinky finger to a grounded case, and then touch a live wire to see if it is hot. As long as the current does not run through their heart or brain, they are not injured. But that only works on voltages of 300 volts and less. Otherwise you could burn off a finger or hand. But it would not kill you.MSEE, PEComment
FWIW, those canny electricians are also careful not to touch two wires at different potentials at the same time! If they do that the lack of a ground will not save them.SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment
Grounding objects is great, but people have no clue what it does. Many electricians have no clue. There are 7 reason to ground something.
- Provide a planned path for lightning to discharge into earth.
- Accidental contact with utility High Voltage lines, or utility primary to secondary faults during storms or accidents
- Provides a discharge path for static electricity.
- Minimize touch potential of metallic frames, raceways, and equipment chassis under fault conditions.
- Provides a PLANNED FAULT LOW IMPEDANCE fault path back to the source to allow fusses and breakers to operate efficiently and quickly.
- Provide a signal reference level.
- Short out cable capacitance in large industrial systems.
Also note Ground does not necessarily mean earth. It can be earth or any body in place of earth like your car, boat, plane, or spaceship. Under normal operating conditions a ground does absolutely nothing in a residential application. In your home it is used to keep lightning and utility high voltages out of your house, and a cheap efficient way to have over current protection devices like breakers and fuses.
Industrial does not use grounded systems, the use Un-grounded Delta, or Floating systems. They do so for two main reasons. Grounded systems are prone to unnecessary outages, and dangerous to personnel working with such high voltages. Imagine how much it cost and down time in something like a glass or plastic extrusion operation or a refinery and the power goes off. It would take you several days to clean out the equipment and get it back on line, not to mention can even destroy the equipment. Hardened cold glass in a extruder destroys the extruder it. Or loosing a million barrels of raw petroleum that had to be burned off because you could not distill it. People in industrial applications can die if power is lost.MSEE, PEComment
