To all the 12v Solar experts out there, I need your advice.
I'm in the process of ordering all the stuff I need to set up my solar panels on my caravan. I've done a heap of research into voltage drops, wire sizes, etc etc. before I go ahead and order the wire I just want to get advice Im doing the right thing.
* I will be mounting a 200W solar panel on the roof of my van which will have 4m of cable to the battery.
* I will also be buying a separate 160W folding solar panel which will have a 12m Cable so I can manually put in the sun in case of shade issues with the other panel etc.
* I have plans to possibly add another 160W folding panel later on.
I calculate I will need a 20amp solar controller for the first 2 panels and 30amps if I use 3 in the future so I have purchased a 30amp solar controller.
I have read that you shouldn't have more then 2% voltage drop in the solar wiring. Therefore 18V * 0.02= 0.36V
Im looking at 6B&s and 8B&s wiring fo the 12m cable.
(AWG6) 6B&S = 13.3mm2
(AWG8) 8B&S = 8.3mm2
(AWG11) 6mm = 4.2mm2
The formula Im using for Voltage drop is (from redarc website):
Vd=(length wire * Amps * 0.017) / wire mm2
So for the 200W panel with 4m cable run I calculate a voltage drop as follows:
Vd for 8B&S (200w@4m) is 0.09
Vd for 6mm (200w@4m) is 0.16
for the 160W panel with 12m cable run I get
Vd for 6B&S (160W@12m) is 0.13
Vd for 8B&S (160w@12m) is 0.22
By looking at the voltage drops all of them are under the 0.36V drop so my conclusion is I could use either wire gauge for both cable runs.
For example the cost of 12m of 8B&S is $70 or for 12m 6B&S is $95. Would I be better of getting the 6B&S for the little bit extra or is the 0.1V difference between the wires negligible and should I just save the $25.
If I did get the 6B&s 12m wire if I added another 160w panel later (320w total) I calculate the voltage drop of both these panels as being:
Vd=(12 * 17.8amps * 0.017) / 13.3 = 0.282v
This is also less than the 2% voltage drop (0.36v) that was recommended so my calculations would say that 320w solar panel over 12m with 6B&S wire is ok. Is this correct or is that voltage drop getting too high.
The other option Im looking at is going thicker cable again (3B&S) which starts getting very expensive or running separate cable for each solar panel (Either 6B&S or 8B&S for each).
Any recommendations on wire size would be greatly appreciated and if any of my calcs are wrong please let me know.