Hello folks. I would like your help to review the system I intend to purchase to power a water pump in a remote location in Nigeria. I will include what I am buying and also why I am buying to make sure I truly understand sizing a solar set up.
What will be powered: Water pump is 70w, 1amp and will run 24/7.
Solar Kit Components
300w mono panel:
70w * 24hr =1.68kw/day * 1.2 (make up for loss) = 2.1kw/day
I need to produce 2.1kw/day with 8hrs of sun power.
2100w divided by 8hrs = 262.5w
300w * 8hrs of sun power = 2.4kw/day
I need to produce at least 263w per hour so 300w will get me what I need.
Renogy 40amp MPPT Charge Controller:
Max input power of 400w. I'll be pulling in below 300w.
I'll have a mix: 24v panel and 12v battery bank. This mppt charge controller can handle the combo???
The water pump is only 1amp. Is this overkill? I plan to get a second and third water pump in a year or 2. Since the water pump only requires 1amp, am I 39amps over what I really need?
Pure sine inverter: I need to run 70w of continuous power so an inverter of 100w is sufficient. Correct? How do I know if I should select a 12v or 24v inverter?
520ah Battery Bank
1680w / 12v battery bank (the water pump is 12v) = 140ah/day.
I want to have a 2 day reserve so... 140ah * 2 days = 280ah.
I don't want the batteries to go below 50% charged so I double the amp hours to 560ah. Based on the rating of the deep cycle battery I decide to purchase, they need to add up to 560ah or more.
Am I missing anything? Is anything wrong?
Thanks for your help.
What will be powered: Water pump is 70w, 1amp and will run 24/7.
Solar Kit Components
300w mono panel:
70w * 24hr =1.68kw/day * 1.2 (make up for loss) = 2.1kw/day
I need to produce 2.1kw/day with 8hrs of sun power.
2100w divided by 8hrs = 262.5w
300w * 8hrs of sun power = 2.4kw/day
I need to produce at least 263w per hour so 300w will get me what I need.
Renogy 40amp MPPT Charge Controller:
Max input power of 400w. I'll be pulling in below 300w.
I'll have a mix: 24v panel and 12v battery bank. This mppt charge controller can handle the combo???
The water pump is only 1amp. Is this overkill? I plan to get a second and third water pump in a year or 2. Since the water pump only requires 1amp, am I 39amps over what I really need?
Pure sine inverter: I need to run 70w of continuous power so an inverter of 100w is sufficient. Correct? How do I know if I should select a 12v or 24v inverter?
520ah Battery Bank
1680w / 12v battery bank (the water pump is 12v) = 140ah/day.
I want to have a 2 day reserve so... 140ah * 2 days = 280ah.
I don't want the batteries to go below 50% charged so I double the amp hours to 560ah. Based on the rating of the deep cycle battery I decide to purchase, they need to add up to 560ah or more.
Am I missing anything? Is anything wrong?
Thanks for your help.