We have twenty 170-watt panels connected in series in two 10-panel strings. The two strings are connected to a Fronius inverter. One of the panels' glass covers has shattered (for unknown reasons). Can I simply remove it, and run one string with 10 panels and the other with 9? Do two-string inverters require that the voltage from each string be equal, or are these types of grid-tied inverters capable of handling strings of differing voltages?
Unequal number of panels in strings?
Collapse
X
-
-
The question is,...
Does your inverter have 2 MPPT inputs, or do the solar strings go into one set of terminals ?
And if it does have 2 inputs, will a shortened string have enough voltage to properly run ?Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister -
You should be fine with unequal panel counts. The Fronius will treat the strings independently.
It would be best to read the Fronius spec sheet to be sure that 9 panel output voltage fits within the window of the Fronius, but if it is like modern Fronius inverters, you'll be fine.7kW Roof PV, APsystems QS1 micros, Nissan Leaf EVComment
-
Thanks for the answers. The Fronius was installed in 2014 and it will work with the 9 panel output voltage.Comment