Just put my rails up today and will be doing the wiring on Friday. I have a 7.5kW system using Enphase IQ7 microinverters on 2 strings. The system is on the opposite side of the house from the MSP. I bought a bunch of conduit but thought, why can't this be done in Romex? It would be a pain to get all the bends in my cramped attic, and it's a 240VAC circuit once it's in the attic. Some Googling showed some debate on this several years back, and the consensus was, yes this is acceptable. So here would be my plan:
Enphase Q-cable -> #10 THWN in JB on attic -> through EMT into attic -> into JB -> to 10/2 Romex -> JB at end of attic -> #10 THWN -> Combiner through EMT
Now, if you agree this is acceptable, how is the EGC run, since my plans spec #8? Can I run 10/2 and a separate #8 wire alongside it? Or should I just run 8/2? If I recall, it's against code to change wire sizes in a JB without a breaker....
Thanks in advance!
Enphase Q-cable -> #10 THWN in JB on attic -> through EMT into attic -> into JB -> to 10/2 Romex -> JB at end of attic -> #10 THWN -> Combiner through EMT
Now, if you agree this is acceptable, how is the EGC run, since my plans spec #8? Can I run 10/2 and a separate #8 wire alongside it? Or should I just run 8/2? If I recall, it's against code to change wire sizes in a JB without a breaker....
Thanks in advance!