I have a power house for my solar system (not yet installed) which will contain the batteries, inverters and charge controllers. The building is 10'x12' and divided down the middle by a wall. The batteries will be on one side and the electrical equipment will be on the other.
My solar wiring diagram has two 2/0 cables connecting each battery's terminal to that of the next (four cables per battery.) At the end of the string (twenty-four 2-volt batteries) I will have 48 volts and 2050 aH. The diagram shows one 1000 MCM cable for the positive and one 1000 MCM cable for the negative, connecting the battery bank to the battery combiner box.
I've already bought the 2/0 cables (rather than 500 MCM cables to use in their place) but I'm wondering: do parallel cables violate the NEC?
I'm wondering if two 300 MCM cables could replace the 1000 MCM cable, which I haven't yet purchased.
The length of the 2/0 cables is 12 inches. The 1000 MCM cables would probably be about three feet long.
Should I return the 2/0 cables and locally source some 500 MCM? The place I got the 2/0 cables doesn't have anything bigger than 2/0.
Thanks!
Jim
My solar wiring diagram has two 2/0 cables connecting each battery's terminal to that of the next (four cables per battery.) At the end of the string (twenty-four 2-volt batteries) I will have 48 volts and 2050 aH. The diagram shows one 1000 MCM cable for the positive and one 1000 MCM cable for the negative, connecting the battery bank to the battery combiner box.
I've already bought the 2/0 cables (rather than 500 MCM cables to use in their place) but I'm wondering: do parallel cables violate the NEC?
I'm wondering if two 300 MCM cables could replace the 1000 MCM cable, which I haven't yet purchased.
The length of the 2/0 cables is 12 inches. The 1000 MCM cables would probably be about three feet long.
Should I return the 2/0 cables and locally source some 500 MCM? The place I got the 2/0 cables doesn't have anything bigger than 2/0.
Thanks!
Jim