A friend asked me if he could wire in series a 12v 100w panel to a 24v 300 panel .so to all the experienced people here I ask is it possible and would it the same as wiring a same volt panel?
12v to 24v series
In series, the voltage difference doesn't matter, they all add up. Whatever controller the series string is wired into would need to be compatible with the higher voltage. For those particular panels, the problem is that they don't produce the same current, so the string won't produce as much as they would each make individually.CS6P-260P/SE3000 - http://tiny.cc/ed5ozx -
Unfortunately the "12v" panel could drop the voltage of the 24v panel and not be totally added..
Are you using an MPPT or PWM CC?Comment
in Series, Voltage adds, and amps should be within 10% of each other (amps are limited by the lowest amp panel)
in Parallel, amps add , and voltage should be within 10% of each other. (Voltage limited to the lowest voltage panel)Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
Great info he has a ul rated grid tie inverter with mppt. he has 12v 2000 watt hooked in series then he has 24v 1200w hooked to an eBay grid tie inverter.I believe his ul rated inverter is 8000w .Comment
What is the make and model of the UL rated and eBay "grid tie" inverter? Be careful that some of that equipment are not truly UL Listed and can't be legally used in the US.Comment
