How many amps circuit braker should i use for 5KVA INVERTER? Ur ans re welcomed
Sizing circuit brakers for 5kva inverter
Collapse
X
-
-
Is the breaker for the DC input (what DC voltage?)
or for the AC output (What AC voltage, 120V or 240V)
Whatever size breaker you use anywhere, the wire HAS to be rated at a higher amp value than the breaker:
30A breaker needs 10 ga wire (or even larger)
You want the breaker to pop open before the wire heats up and starts a fire.
here's a copy of the official table (note some wire gauge changes depending on the insulation)
Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||