Splicing DC conductors of PV circuit (PV wire #10) in JBs (on the roof) with THHN (#10) for going to the home run in the conduit. And using wire nuts for splicing..Big deal?
Thx
Splicing DC conductors of PV circuit (PV wire #10) in JBs (on the roof) with THHN (#10) for going to the home run in the conduit. And using wire nuts for splicing..Big deal?
Thx
Wire nuts are never a good solution to splice wire in an outside junction box. They will eventually come apart and cause issues.
Better to use a wire termination equipment such as the Burndy Unitap that Amy suggested.
Or even better, instead of a junction box, use a Pass thru box like Wiley Electronics Acme Conduit Entry (ACE) Pass-Through Enclosure or on an asphalt roof, a SolaDeck 0786-3R5 for pass-thru and roof penetration into conduit.
Unitaps are more expensive than wirenuts for a reason. Unitaps are cheaper than a fire.
Not sure if you are getting the system inspected, but most AHJ don't like wirenuts there, they like Unitaps.
It sounds like you have answered your own question. Use the wire nuts if that is what you want - you will have to determine for yourself if it is a big deal.
However wanted to hear electricians, saying something about prevent dc arching, and about long term of wire nuts splicing (that are on the market right now) like 15-20 years. Inspection here won't go on the roof, but I'm wondering about quality of installation.
Thx
Wire nuts are NOT for exposed locations. Maybe for a low power lawn sprinkler system, but not utility power where they see weather hot cold cycles, moisture condensing on them....... Wire nuts OK indoors on lower amps wiring.
Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
Wire nuts are not permitted in damp or moist locations for power and lighting. End of story. There is no good reason to have any splices. Would indicate a poor design and/or workmanship.
Wire nuts are not permitted in damp or moist locations for power and lighting. End of story. There is no good reason to have any splices. Would indicate a poor design and/or workmanship.
It's not so much a splice as transitioning from PV Wire from the panels to THHN in the conduit to inside. Which requires a pass-thru box, not wire nuts. I don't have my code book on me, but I thought PV wire was not supposed to go in conduit, thus the transition. I may be wrong, it could just be a cost thing, THHN is much less $ than PV Wire. Either way, don't use wire nuts in a moist location exposed to heat/cold. They will fail.