Hello all,
As an avid RV'yer, I have developed an interest in solar panels so that I can go boondocking. Last year, I had the opportunity to buy 6 siemens sp75, which have a Vmp of 17.1 volts. They are connected in parallel to a "commercially customized" charge controller, and are charging a bank of 12v batteries of 460 amp/h.
Because I was looking at upgrading my charger to an MPPT one, I had the opportunity to buy a package which had 4 solar panels and the Flexmax 80. The package is 2 X Kyoceras KD205GX-LPU, and two Suntech STP170s-24/ab-1.
As I am trying the best way to hook them together, I realized that their Vmp was much different, even though their nominal voltage is 24v. Indeed, the Kyoceras have a 26.6 Vmp while the Suntech have a 35.2 Vmp.
Should I hook all 4 panels in parallel thus losing on the Suntech (which would be brought down to 26.6v) or should I wire the Kyoceras in Series, the Suntech in series, and then parallel them? The only reason I'd want to do that would be to minimize the voltage drop I am getting on my 60 ft 10awg wire run I have between the panels and the Flexmax, as it would cut it in half.
Also, what might be the most optimal way of using them along with the Flexmax?
I am also thinking of using the Aux output on the Flexmax to diverse a load to a small space heater when my batteries are full. How hard is that? I already have a solid state relay that is good for 25 amps AC...
Thanks in advance,
As an avid RV'yer, I have developed an interest in solar panels so that I can go boondocking. Last year, I had the opportunity to buy 6 siemens sp75, which have a Vmp of 17.1 volts. They are connected in parallel to a "commercially customized" charge controller, and are charging a bank of 12v batteries of 460 amp/h.
Because I was looking at upgrading my charger to an MPPT one, I had the opportunity to buy a package which had 4 solar panels and the Flexmax 80. The package is 2 X Kyoceras KD205GX-LPU, and two Suntech STP170s-24/ab-1.
As I am trying the best way to hook them together, I realized that their Vmp was much different, even though their nominal voltage is 24v. Indeed, the Kyoceras have a 26.6 Vmp while the Suntech have a 35.2 Vmp.
Should I hook all 4 panels in parallel thus losing on the Suntech (which would be brought down to 26.6v) or should I wire the Kyoceras in Series, the Suntech in series, and then parallel them? The only reason I'd want to do that would be to minimize the voltage drop I am getting on my 60 ft 10awg wire run I have between the panels and the Flexmax, as it would cut it in half.
Also, what might be the most optimal way of using them along with the Flexmax?
I am also thinking of using the Aux output on the Flexmax to diverse a load to a small space heater when my batteries are full. How hard is that? I already have a solid state relay that is good for 25 amps AC...
Thanks in advance,