With only a 12volt 140Ah battery system I would look for a smaller inverter in the 400watt range max. You loads are small so using that 1000 watt inverter will just use battery capacity even if no load is on.
With those 57watts of lights and that battery system you can probably get away with running them about 7 hours a night. If you add the trickle charger and depending on what wattage it really consumes you can run those light only about 6 hours a night.
The problem is the low Ah rating of your batteries even with 4 wired in parallel. That system gives you about 1680 watt hours total and you should not discharge your batteries more than 25% each day. So 25% of 1680 watt hours comes to about 420 wh. That gets you about 6 hours with a load of 70 watts.
I just realized your batteries can not handle a 45 amp charge. They are too small for that and will get hurt. Use only one of those 260 watt panels not both.
With those 57watts of lights and that battery system you can probably get away with running them about 7 hours a night. If you add the trickle charger and depending on what wattage it really consumes you can run those light only about 6 hours a night.
The problem is the low Ah rating of your batteries even with 4 wired in parallel. That system gives you about 1680 watt hours total and you should not discharge your batteries more than 25% each day. So 25% of 1680 watt hours comes to about 420 wh. That gets you about 6 hours with a load of 70 watts.