UPS batteries for grid-connected emergency battery backup - Use deep cycle or not?
  • lkruper
    • 892
    I have heard it discussed that one cannot use UPS batteries for Renewable Energy storage because they are not designed for repeated cycling.
    What about battery backup for emergency usage? Would UPS batteries have some sort of advantage over deep cycle batteries such as price or performance?
    It is likely that if I put batteries in place to supplement the emergency generator at my cabin that I might want to add a battery bank just in case there is a prolonged outage (more than a few days). I think I can get my daily load down to 800 watt hours or so.
    I have not had any power problems for 5 years and it is possible I might not have any for the next 5, but this is kind of like insurance.
    Perhaps "CANNOT" is a bit of of over statement, replce with "Should Not" be used for daily cycle service. For one simple reason, UPS and Telecom batteries were not designed daily cycle service, they are designed as Emergency Stand By service operating as Float Service. The batteries are designed for very high discharge rates. To get that you have to sacrifice cycle life. Pushed into cycle service you would be good to get 200 cycles.
    However can you use them?
    Yes now that you know
    • lkruper
      • 892
      Thanks, Sunking.
      What batteries should I consider for my application? Batteries that will sit charged except for "emergency" drills and when utilized may be used for one day or two weeks every couple years at the most?
        Put it to you this way and then you decide.
        Telecom batteries are top notch high performance batteries and extremely expensive. Even if I needed a high discharge rate I would not use them new because of expense vs time, literally 1/2 to 1/3 the cost using something else better suited to the application. Telecom is on steroids and a special breed of battery. The are built to go fast, and fast cost money.
        However if you have an application where you only need say 10 cycles a year, batteries at or below salvage value, and willing to take a calculated risk might work out for a year or two.
        Allow me to guess. You know a guy who has access to salvage telecom batteries cheap right?
        • lkruper
          • 892
          No, I have no contacts and have no knowledge of salvage telecom batteries. However I know I have seen battery replacements for UPS systems for sale and wondered if they would be better suited to my requirements than RE batteries.
          For what I want, with the projected limited use of the batteries, I would like them to last 10 years, if possible.
          However, if you are recommending salvage telecom as inexpensive and useful, I would consider them because I am told I will probably destroy my first set of batteries.
          • jony101
            • Jun 2014
            • 99
            i had a 145 ah telecom agm battery, it was a big heavy battery and I used it everyday connected to my 240 watt panel. Even though it worked performance was not good. Even with minimal use every morning it was reading 12.2 12.3 volts. i use it for about a year before I decided to upgrade to something better.
            I replaced it with a kinitek kh2000, 102 ah agm. A smaller lighter battery. With the same use, this battery is 12.5 12.6 in the morning. A very big improvement. After a year of use the battery still reads 12.9 when its fully charged.
            In a emergency, I dont think the telecom battery would provide enough power before dying out. They might be cheaper and because of there size and weight look like they are powerful but from my experience I would maybe buy one and see the performance before committing to buy a large qty.
            • lkruper
              • 892
              The only reason I thought about UPS batteries, is because I had heard that it is not recommended to use them for RE applications. If the converse were true, then I wanted to investigate whether or not they would be a good choice for my application, which is grid-tied stable power but for emergency outages.
              However, in an emergency I would want them to perform like RE batteries. I could live with less cycles ( because I won't need them) but would want those cycles to have the same effectiveness as RE batteries.
              In looking online at some batteries advertised for Telecom/UPS it appears they are designed for fast response at higher amperages. One, MK, only gave performance up to 60 minutes. I would want my batteries to perform over-night. So it appears that I have eliminated these types of batteries for what I am trying to do.
              Now I am wondering again, if a good compromise might be to get a good RE battery but spec it out to use 80% of capacity with the knowledge that I won't need that many cycles. I floated that idea here in the last few weeks on the basis of the %DOD/Cycle charts provided by the manufactures. However I was cautioned that even though the manufacturers gave that performance spec on their sites, one could not count on getting the advertised # cycles at the 80% discharge load.
              • PNjunction
                • Jul 2012
                • 2179
                80% discharge for lead-acid can sometimes be unrealistic due to voltage drop. Beyond 50%, the voltage drop is enough that inverters and the like start to run hot and inefficient, some gear goes intermittent, displays flash, that kind of stuff.
                In the early days, agm marketing was that they were good to 80% but in the real world, the voltage drop put everyone back to designing around no more than 50%.
                Napkin calc: With 800 wh, and assuming a 12v cabin setup, (800w / 12v = 66.6a drawn total) that means at least a 120ah rated battery.
                Many choices depending on how willing you are to maintain / replace them. But you want 10 years (possibly unrealistic under the best conditions) and have a genny to provide some real recharge after a deep-discharge event.
                Personally, I'd recommend an Odyssey PC-2150 / 2250 agm for your load requirements stated at this time. BUT you MUST be able to accurately control the float voltage to satisfy the warrantee, which in this case is 13.5 to 13.6v. NOT 13.2, nor 13.8v !! That is a *single* Odyssey, not a bunch of lower capacity cells paralleled together. Odyssey's do well when put into standby service such as you desire IF you follow their charging regimen. You may not get exactly 10 years out of them due to simple aging, but if any battery can do it with proper maintenance, they will. Essentially the Odysseys are consumer level Enersys batts, which of course make high-end commercial setups, but even at the consumer level their high voltage under load and low internal resistance allows them to handle huge surges and so forth. Expensive, so be sure to get your load requirements right off the bat.
                Make regular tests of the system, say once a year to 50% DOD.
                Or you could use a bunch of starter batteries if you were willing to trash and replace them every so often. Choice is yours....
                  UPS batteries are high performance batteries. They can be be charged and discharged at much higher rates then a deep cycle. Their discharge curve is almost identical top deep cycle, they just do not sag like deep cycle. What you give up is a lot of cash and cycle life. They cost 2 to 4 times a deep cycle FLA and only last 1/10 to 1/5th as long. Instead a 1 Kwh battery costing $200 and lasting 1500 cycles you pay $$400 and get 150 cycles. But they will run circles around a deep cycle FLA for the first 100 cycles or 5 years whichever occurs first.
                  • lkruper
                    • 892
                    Thank you! I am very impressed with what I am reading in their manual (http://www.odysseybatteries.com/docs...M-002_1014.pdf). They don't seem to be overly concerned about the occasional really deep cycle and also bill this as having an 8-12 lifetime in standby mode.
                    I also like the fact that I can get them on Amazon and they offer Prime shipping. I would be inclined to buy their charger as well and see they make a 50A charger (although I am not finding it for sale anywhere... some saying it was discontinued).
                      Odyssey are very popular batteries for DIY Ev's, Robotoics, and consumer grade UPS. They have about 400 to 500 cycles, or 4 to 5 years in Stand-By. Whichever comes first. So in Stand-By Emergency Float service expect only 3 to 5 years.
                      Odyssey AGM is like Telecom batteries a high performance AGM. With its very low Internal Resistance means you can charge then real slow or real damn fast.
                      If we are talking about 2150 you can charge them as slow as 10 amps, or as fast as 300 amps, and anything in between. For the 2250 can be charged as slow as 10 amps, or as fast as 375 amps.
                      What you really need to ask yourself is: Do I need to pay the premium and need a battery that can supply a C/2 discharge rate?
                      Because depending on where you buy the 2150 and 2250 are going to cost you roughly $0.342/wh for a battery with a 24 month warranty. You can get a premium line Trojan T-105RE 5 year battery for $0.12/wh or 1/3 the cost of an Odyssey, 5 year warranty, and can easily handle a C/4 discharge current with an R= .0035 Oms. A pair of T-105RE has a capacity of 2.7 Kwh for $300, vs 1.2 Kwh for an Odyssey PC2150 @ $330.
                      So back to your original question. Why not use Telecom Batteries.
                      Answer is a big NO for cycle applications because of short cycle life. A definite MAYBE for Stand By Service if you can justify the performance and short life span.
                      Odyssey are great batteries, number 2 in my AGM book only second to Concorde Sun-Extender AGM which runs circles around all other AGM batteries including Odyssey. Concorde like Odyssey, you really need to justify the expense. Because at end of life is going to cost you some 400 to 600% more than FLA. The Odyssey PC2150 can only deliver 50 amps without excessive voltage sag, but can only do so for 40 minute with a 100 AH rating. The Trojan can deliver the same 50 amps for 3 hours at less cost with a battery warranty and longer cycle and calendar life.
                      So do your homework before you start dropping cash, because there are better alternatives.
                      • lkruper
                        • 892
                        Thanks, I was wondering about Sun Xtender as I just had a page up selling them and it appears I can get a bigger battery than Odyssey for less money, but I have not really shopped.
                        Another reason I was considering AGM instead of FLA was your sticky which shows how to design a battery system. The insolation number for my location goes from a low of 2.82 to a high of 7.36. The winter numbers give a higher panel size and a charge rate of C/4. ( BTW, thanks for that sticky, after I read it a few times and made my own spreadsheet it advanced my knowledge considerably. ) That means I need to use AGMs. However as I figured out (hopefully correctly!), if one increases autonomy and thus the battery bank size it is no longer necessary to use AGM.
                        In that scenario one gets to use FLAs at 1/2 the cost.
                        Another thing I need to consider is that in my location I will probably lose a few hours sunshine in the morning because of trees and another at the end because of a canyon. I think I retain most of the highest sunshine hours. However this also means I must compress my charging into fewer hours which again supports either a higher rate of charge than FLA can take or a bigger bank.
                        For a small system like mine, I am not all that concerned about spending $500 on batteries (when I get around to it), because that is about what I spent for my inverter/generator.... its another tool that I won't need to use that much but which I will be really glad I have if I need it. I also like the idea of learning how to maintain FLA batteries.
                          2.25 Sun Hours is the threshold. Example lets say you need 300 watt hours, mppt, and 2.25 sun hours.
                          A 300 wh daily load requires 12 volt 125 AH battery. With 2.25 sun hours required a 200 watt panel. A 200 watt panel using a MPPT controller generates up to 15.7 amps. 15.7 amps on a 125 AH battery is C/8.
                          • lkruper
                            • 892
                            2.25 is the threshold for 5 day autonomy. I estimate I can get by in an emergency with 768 kWh and want the battery to last over-night so that I don't have to run the generator at night. So I planned for 2X autonomy with 50% DOD max which requires a panel of least 408w (insolation of 2.82) and a battery of 128 ah at 12v (or 64 at 24v). This is a charge rate of C/4. However as I said earlier, I could spend the same amount of money on FLA batteries and increase the autonomy to 5 (which is hard-wired in your sticky) and use FLA.
                            Actually, looking at this a bit closer at 5X autonomy I would need 320AH at 12v and 160 at 24v. I would need to spend as much or more on the 320 FLA as I would on the 128 AGM. Another complication is that I will lose some sunshine in the morning and evening due to trees and canyon. So I might need to further compress my charging into fewer hours to compensate.
                            I am planning my emergency system in phases.
                            1) Install the manual transfer switch for my existing generator.
                            2) Install a battery + charger + inverter to allow for quiet power at night. Plug into manual transfer switch at night and turn off generator.
                            3) Install a panel and CC for possible longer extended outage.
                            • lkruper
                              • 892
                              I am in the process of implementing step #1 of my plan (http://www.solarpaneltalk.com/showth...l=1#post163486) which is installing the manual transfer switch. My recent experience is leading me to believe I will get to step #2 within 6 months.
                              The reason is that I experienced my first power outage at the cabin. Power went out around 5PM and did not get back on until after 1AM. I have not yet had the transfer switch installed ... hopefully this Wednesday. Good news is that I experienced using my 1600w inverter generator with extension cords through the back door and all over the floor. My APC UPS on my DSL modem worked well and gave me 4 hours of internet connectivity until that battery was depleted. I had not connected the generator up because the power company kept stringing me along with false promises all night so around 10PM I connected the generator. Can't wait for my transfer switch.
                              Now I want to plan for phase II which is to have 4 6v T105 batteries (maybe RE) in series for 24 volts to be on standby with a charger connected to grid power and an inverter. To switch over I will cable the inverter to my manual transfer switch. I was able to experience trying to get to sleep with a generator running and don't like it.
                              So my question is, to wire these 4 batteries in series, does it matter how I physically set them up? 4 batteries end to end, side by side or even two side by side above two side by side? Does the length of wire matter in series? Also, I am completely ignorant about connectors. What are the absolute easiest to implement and maintain? I am willing to buy wires pre-made to connect to the batteries.