#1 |
|
Junior Member
|
Pls. clarify or describe in detail about the under mentioned battery bank;
2V/600Ah @ 120Hrs. Now, what would be the battery bank size if 24 above batteries are connected in 48V series system? Second, how long would be the backup time when fully charged, if 3000Watts are drained every hour? Third, if replacement is needed, how many 12V/150Ah batteries are required? |
|
|
|
|
|
#2 | |||
|
Solar Fanatic
Join Date: Feb 2010
Posts: 658
|
Quote:
Quote:
Quote:
__________________
DereckC MSEE, PE |
|||
|
|
|
|
|
#3 | |
|
Junior Member
|
Quote:
---------------------------------------------------------------------------------------- It establishes that better go for 12V/150AH @ C20 rating sixteen batteries to make 48V in series and (48*600) 28,800W rather 2V/600AH @ 120hrs. twenty four batteries to make 48V in series. Am i right? 24 batteries will cost more and consumes more electrolite around 11.3 Ltrs. per battery. Maintainance & space is also more hard than 16 nos. Second, if printed @ C20 or @120hrs. means same rating? |
|
|
|
|
|
|
#4 | |
|
Solar Fanatic
Join Date: Feb 2010
Posts: 658
|
Quote:
Note the 20 hours capacity compared to the 100 hour capacity. At 100 hours it is rated 293 Amp Hours. At 20 hours it is rated 220 AH. No go look at the 4 hours discharge rate we used earlier for your 3000 watt at 48 volt example. It goes all the way down to 143 AH. Sizing to 100 hour discharge rate AH and using the 4 hour rate is over a 100% difference in capacity. For batteries you always want to use a single string if possible. Using Multiple strings takes extreme care in design and operations.
__________________
DereckC MSEE, PE |
|
|
|
|
|
|
#5 |
|
Junior Member
|
Followed your points. Now, how we can calculate Ah capacity down to 1 hr. at our end?
|
|
|
|
|
|
#6 |
|
Solar Fanatic
Join Date: Feb 2010
Posts: 658
|
Look at the manufacture discharge curves or tables like I showed you.
__________________