    Default 1MW system design

    Hey all,

    I've been given the task of pricing out a 1MW solar project. I don't have much of a background in solar system design but I'm trying to understand how a typical system of this size is constructed and what equpiment is needed in order to come up with an accurate cost for a 1MW project. I have a few questions and I was hoping you guys could help me out.

    The panels we will be using for this system have a Voc of 291.4V, Isc of 2.75A and a power output of 530.5 Watts. Maximum system voltage is 1000V.

    What factors should I look at when connecting these panels into strings/arrays? I'm thinkng of putting 2 panels in series to give me a string voltage of 582.8V and then putting six strings in series to go to my combiner (with a 20A rating) with a current of 16.5A.

    What equipment is needed to conect the output from the inverters? Do they just connect to the inverter?

    Do I need a dc dissconnect after each combiner?

    Any input you guys have would be helpful,

    Thanks,
    JT

  2. #2
    Moderator
    Join Date
    May 2009
    Location
    off grid retirement in Northern Calif
    Posts
    7,345

    Default

    Wow ! Awesome ! And so far out of my residential league !

    Generally, with the large installs, you use 3 phase inverter systems, and lots of
    planning with both the city and the utility company.

    That's all I have.
    Since the dawn of time it has been mankind's dream to blot out the sun.
    Montgomery Burns

    "Always listen to experts. They'll tell you what can't be done and why. Then do it."

    spreadsheet based voltage drop calculator:
    http://www.solar-guppy.com/download/...calculator.zip
    http://www.solarpaneltalk.com/showth...oss-calculator

    http://www.mike-burgess.org/PVinfo_2.html

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,
    battery lugs http://tinyurl.com/LMR-BigLug
    Setting up batteries http://tinyurl.com/LMR-NiFe

    gear :
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV || || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

  3. #3
    Junior Member
    Join Date
    Aug 2009
    Posts
    8

    Default

    Haha..thanks. It's very much in the planning stages. I'm just curious to figure out how it works so I can figure out how much it will cost.

  4. #4
    Aussie Bob
    Guest

    Default

    JT,

    Are you an Aussie by any chance?

  5. #5
    Junior Member
    Join Date
    Aug 2009
    Posts
    8

    Default

    Close, Canadian.

  6. #6
    Junior Member
    Join Date
    Aug 2009
    Posts
    8

    Default

    Here's the issues I'm currently scratching my head about...How many combiners do I need? Say I connect 2 panels in series, then I connect three sets of two in parallel for a total of 6 panels on a string. Would I then connect two strings together at a combiner? Or would it make more sense to connect more then two at a combiner? What is considered when combining strings at a combiner? Also, can I connect the outputs from the combiners directly to the inverter or is there another piece of equipment that gets connected in between?

    Any ideas?

  7. #7
    Moderator
    Join Date
    May 2009
    Location
    off grid retirement in Northern Calif
    Posts
    7,345

    Default

    You want to set up series strings to your max (Cold Morning Startup voltage) input.

    Each string is paralleled in the combiner box. You use as many strings as needed to "fill
    your inverter" so you don't have to buy so many inverters. The combiner box should be
    spec'ed for X number of strings. The inverter should have a spec for how many input wires it can accept. Those feed wires come from your combiners. If 3 feed wires, you need 3 combiners. Then you figure what size combiners you need , 3 or 12 circuit.
    Each string, in the combiner, should have it's own fuse or breaker.
    Since the dawn of time it has been mankind's dream to blot out the sun.
    Montgomery Burns

    "Always listen to experts. They'll tell you what can't be done and why. Then do it."

    spreadsheet based voltage drop calculator:
    http://www.solar-guppy.com/download/...calculator.zip
    http://www.solarpaneltalk.com/showth...oss-calculator

    http://www.mike-burgess.org/PVinfo_2.html

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,
    battery lugs http://tinyurl.com/LMR-BigLug
    Setting up batteries http://tinyurl.com/LMR-NiFe

    gear :
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV || || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

  8. #8

    Default

    Hello All, Wow that's a nice project 1MW system, might I ask if it's a local company that's asking or you simply doing this for someone else...to submit on their behalf? I ask because just the design work involved is a fare part of the cost factor so I am wondering how you might do the end cost pricing without all the figures in mind? I'd say you need to simply do the math at about 8-9 per watt and that should cover it...I think, if anyone thinks I'm way off please let me know. I too am having more trouble pricing out projects then anything else involved. So I've started using simple watt times dollar amount to get end result cost of project. Seeing there are so many different models, manufactures and add ons...it's hard to do prior to being awarded the job. You should keep in mind that an over ride should be in order here...of at least 15% or so!

  9. #9
    Junior Member
    Join Date
    Aug 2009
    Posts
    8

    Default

    Yes, the company I work for is planning on funding the project. They have asked me to look at the project and see if it would be viable. They have a particular panel they want to use (see specs in the first post) but everything else needs to be priced out. I'd love to go to them and say it'll cost $8 bucks a watt but they will want to see the break down. So in the mean time I'm trying to learn as much as I can about how this type of project is desgned and put together.

  10. #10
    Solar Skipper
    Join Date
    May 2009
    Location
    Jakarta [Lat:06:08South Long:106:45East] Indonesia
    Posts
    657

    Default

    Quote Originally Posted by JTSOLAR View Post
    the task of pricing out a 1MW solar project.
    The panel:
    Voc of 291.4V,
    Isc of 2.75A and
    power output of 530.5 Watts.
    How is it getting on?
    1MW = 1,000KW = 1,000,000W
    Need at least 1,886 panels.
    Space for panels only: 5,000m2 at least. Assuming every 1m2 panel produce 200w.
    Thought, it is not the "on roof system".